How to calculate PF capactors for a connected load?
Answers were Sorted based on User's Feedback
Answer / ramji
First calculate the actual KVAR load.Then calculated the
actual PF.Then as per required PF, calculate the KVAR to be
added.This is the value of capacitor bank to be shunted.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / g parsaram reddy
capacitor bank selection base on the connected load
ex - 500kw load formula is kvar = kw ( tan cos-1pf) - (tan cos-1pf)there is power factor taken lower and higher valu , ex2 kvar= 250(tan cos-1 0.8)- (tan cos-1 0.96)step2 kvar=250(tan36.36-tan16.26) than 250(0.74-0.29) than250(0.45)than kvar=114.5this is required
Is This Answer Correct ? | 0 Yes | 0 No |
What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)
17 Answers Alstom, Call Centre, EDC, HCL, Procon Engineers,
why transformer rating is expressed in kva.
basic princple of induction and synchronous motor
Electricty is generated at around 16kV, then step up to 220kV for transmission then steped down to power transformers then DTs and then through the LT n/w it reaches the consumer end. At the consumer end 230V supply is required. So, why is electricity not generated directly at 230V and transmitted?
What is C-factor?why it is required to consider in fault short circuit calculations?
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
What is order of the system?
what is the carona effects meaning in HT line transmmission system
what is the safety of VCB.
5 Answers Nagarro, Roto Power, RotoPower,
what is load balancing. what maximum load diffence is allowed between phases.
What is the difference between a verilog task and a verilog function?
railway exam in asst loco pilot old test paper
25 Answers Indian Railways, Loco Pilot, RRB, Southern Railways, TATA, Vimal,