if one of the phase is failed to 3 phase IM. what will happen?
Answers were Sorted based on User's Feedback
Answer / b2
it will be run but not for mor time and after some time it
will be burn out
Is This Answer Correct ? | 16 Yes | 0 No |
Answer / abhishek sinha
motor runs for some time with less speed because one of the
phase is gone and current increases in two phases,after
some time if no protection act than motor will burn.
Is This Answer Correct ? | 12 Yes | 0 No |
Answer / shishir dubey
if one of the phase of induction motor is failled then it
will rotate but it draws higher current from the supply
mail and if insulation is poor or not able to withstand
the supply current then after some time it will burn.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / jack
It will run for few second after that relay will trip becous High current will flow in two other phases so that's why our motor will not burn.😊😉
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / paddu241
It will continue to rotate with synchronous speed.
Is This Answer Correct ? | 4 Yes | 13 No |
Shall I use 40A semiconductor Fuses in 32 A SFU ? Frame size is same. What Happen if Fuses burn on SFU?
tell me working of air circuit braker.
why we use salt for earthing?
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
what is stator inter turn fault?
In all the generators, the excitation supply is DC. What is the significance of DC excitation? What will happen if AC supply is given as excitation supply?
what do you mean by class PS CT and what are technical details needed for calculating it?
How the real power output is controlled in a Generator?
What is core CT & it's function?
why do transformer make a sound
why surge suppressor in vaccum circuit breaker and it is only in motor feeder why not in tranformer feeder?no surge suppresor in ocb in motor feeder?
What is the power rate of power transformer?