My dear friends,
First of all i want to introduce myself as transformer engr
having 12 years of experience in transformer field. Now in
reply of your question, if u r asking about Name Plate of
transformer, VA = 1.732 * V * Amp
Suppose In Name Plate,
HV Volts mentioned 11000 V, HV rated current mentioned 5.25
Amp, Than Transformer capacity is
1.732 * 11000 * 5.25 = 100023 VA = 100 KVA.
In the same name plate,
LV Volts mentioned 433 V, LV rated current mentioned 133.34
Amp, So Transformer capacity is
1.732 * 433 * 133.34 = 99999 VA = 100 KVA.
If you are asking about to decide transformer capacity, u
hv to calculate your total load + future expansion load.
Than you can take decision about ur required transformer
capacity.
| Is This Answer Correct ? | 48 Yes | 5 No |
the kva rating can be determined using the formula
kva=power supplied(in KW)/power factor.
so if the transformer is feeding a load of 100MW industrial
load. then the KVA rating of transformer to be used has to be
100/.85=117.647mva
we haver assumed the power factor for industrial load to be .85
| Is This Answer Correct ? | 45 Yes | 9 No |
the kva of an transformer also depends on form factors.
the usage of kva 11,33,66kva all depends on form factor
as 1.11.
| Is This Answer Correct ? | 12 Yes | 9 No |
First Calculate Kw Load of the plant or system which is connected to that transformer.Load is not directly calculated but calculated accordingly as per plant requirement like Continuous,Intermittent & Standby. After calculating the total load of the System in Kw.For calculate KVA of the transformer we use the Formula
KVA Load of the Tranformer - Total Plant Load Connected to transformer ( In Kw) / Power Factor
For Easy calculation ,we take PF value as 0.8.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saravanakumar
This is the formulae for that, KVA=KW/P.F (At the time of
load calculations we should considered the power factor is
0.8 only.)
| Is This Answer Correct ? | 3 Yes | 10 No |
it is very simple by knowing the formula is kva=kw/pf then
applying the formula where kw=1oo thne pf is normaly is
0.85
therefore kva=100/0.85
117.647M VA
| Is This Answer Correct ? | 5 Yes | 14 No |
Can a 5 core cable one end with a 32A 3p+N+E plug and the other end 32A 3p+E be used on a generator?
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
In Single Phase AC Supply,If Voltage between Phase and Neutral is 230V means what will be the Voltage between Phase and Earth?
define power quality
What is the operating principle of turbo-generator.
how to calculate no load losses units comsumed by transformer
WHAT HAPPEN IF LT SUPPLY 415 V FED TO THE HT 3.3KV MOTOR
What happens if the secondary of the transformer is shorted?
give me battery AH calculation in U P S
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
pls send previous bhel electrical papers
What is the different between buchholz relay and pressure relief device?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)