My dear friends,
First of all i want to introduce myself as transformer engr
having 12 years of experience in transformer field. Now in
reply of your question, if u r asking about Name Plate of
transformer, VA = 1.732 * V * Amp
Suppose In Name Plate,
HV Volts mentioned 11000 V, HV rated current mentioned 5.25
Amp, Than Transformer capacity is
1.732 * 11000 * 5.25 = 100023 VA = 100 KVA.
In the same name plate,
LV Volts mentioned 433 V, LV rated current mentioned 133.34
Amp, So Transformer capacity is
1.732 * 433 * 133.34 = 99999 VA = 100 KVA.
If you are asking about to decide transformer capacity, u
hv to calculate your total load + future expansion load.
Than you can take decision about ur required transformer
capacity.
| Is This Answer Correct ? | 48 Yes | 5 No |
the kva rating can be determined using the formula
kva=power supplied(in KW)/power factor.
so if the transformer is feeding a load of 100MW industrial
load. then the KVA rating of transformer to be used has to be
100/.85=117.647mva
we haver assumed the power factor for industrial load to be .85
| Is This Answer Correct ? | 45 Yes | 9 No |
the kva of an transformer also depends on form factors.
the usage of kva 11,33,66kva all depends on form factor
as 1.11.
| Is This Answer Correct ? | 12 Yes | 9 No |
First Calculate Kw Load of the plant or system which is connected to that transformer.Load is not directly calculated but calculated accordingly as per plant requirement like Continuous,Intermittent & Standby. After calculating the total load of the System in Kw.For calculate KVA of the transformer we use the Formula
KVA Load of the Tranformer - Total Plant Load Connected to transformer ( In Kw) / Power Factor
For Easy calculation ,we take PF value as 0.8.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / saravanakumar
This is the formulae for that, KVA=KW/P.F (At the time of
load calculations we should considered the power factor is
0.8 only.)
| Is This Answer Correct ? | 3 Yes | 10 No |
it is very simple by knowing the formula is kva=kw/pf then
applying the formula where kw=1oo thne pf is normaly is
0.85
therefore kva=100/0.85
117.647M VA
| Is This Answer Correct ? | 5 Yes | 14 No |
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
what is difference between neutral and ground wire?
Dear all, I'm manikandan I have done by DIPLOMA EEE from 2011 , I have 5 years of experience from Power plant instrumentation field , which one field is give long life & which one field is best ,I confused a lot and also I'm studying AMIE, can I choose which department from Section B examination? pls tell me
Why Humming noise originated in Starter motor and how it was generated ?
For a three phase induction motor, what will be the effect on motor if the neutral of the system is shifted to say 20 deg.?
what is hysteresis loss?
comparision between ACB and VCB
how to calculate cable size for the motor
Why PS class CT is always preferred for Differential protection?
wat is d diffr btw shunt coil and trip coil in VCB?
PLZ EXPLIN ABOUT CLASS PS CLASS CT .WHY THEY R DESINED AND FOR WHAT PURPOSE?WHY OTHER CT CANT BE USED AS PS CLASS CT? EXPLAIN IN SIMPLE LAUNGAGE IF POSSIBLE PLZ GIVE CIRCIT DIAGRAM?EMAIL-RAJ_SINGH_0376@SIFY.COM
what is brushless alternator?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)