Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why Transformers power mentioned in KVA?. and why Generators
and Motors power mentioned in KW?.

Answers were Sorted based on User's Feedback



why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / nithi

we can design the transformer for some rated voltage &
rated current ,power factor depends on the load.so,we
cannot predict the p.f. while designing the transformer.
But in the case of generator ,it has to supply real
power (depends on the capacity of the prime mover)& some
amount of reactive power to the system (depends on the
rating of exciter).that's why generators are supplied with
the name plate details including p.f.,kva rating & kw
rating.
in case of motor,it has to take some hp(kw) load
(real power) ,for that it uses some amount of power for
producing the magnetic field (magnetizing power--reactive
power).so,during the design itself we have idea about how
much of load the motor should take (hp load).This is the
reason why the motor is rated in kw,p.f..

Is This Answer Correct ?    11 Yes 0 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / lokesh

copper losses of a transformer depends on CURRENT and irons
of a transformer depends on VOLTAGE not an phase angle
between voltage and current. that is why transformer rating
in KVA not an KW.

Is This Answer Correct ?    13 Yes 4 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / sravani

we can design the transformer for some rated voltage &
rated current ,power factor depends on the load.so,we
cannot predict the p.f. while designing the transformer.
But in the case of generator ,it has to supply real
power (depends on the capacity of the prime mover)& some
amount of reactive power to the system (depends on the
rating of exciter).that's why generators are supplied with
the name plate details including p.f.,kva rating & kw
rating.
in case of motor,it has to take some hp(kw) load
(real power) ,for that it uses some amount of power for
producing the magnetic field (magnetizing power--reactive
power).so,during the design itself we have idea about how
much of load the motor should take (hp load).This is the
reason why the motor is rated in kw,p.f..

Is This Answer Correct ?    3 Yes 0 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / tapan k ghosh

The output expected from a generator or transformer is
electrical output. Electrical output contains both active
and reactive components and hence these equipment are rated
in terms of composite power,kVA i.e.sqrt(active2+reactive2).

Output expected from a motor is motive power i.e. active
one and hence motor is rated as kW.

Is This Answer Correct ?    1 Yes 1 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / iyswarya sithanathan

The convention is that source power is mentioned in KVA and load power to be mentioned in KW.

Is This Answer Correct ?    0 Yes 0 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / nilesh chavan

The rating of transformer is given in KVA instead of KW
because total transformer loss depends on VA.

Is This Answer Correct ?    0 Yes 0 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / rajneesh

Transformer has apparent type power while any machine has
the power of active type.

Is This Answer Correct ?    1 Yes 4 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / yogesh

Transformer and genrator PF depends on the nature of
connected load ( Motor ), But motor has its own fixed Power
factor

Therefore Transformer and genrator capacity shown in KVA (
Without PF ) and motor Capacity shows in Kw ( with power
factor )

Is This Answer Correct ?    3 Yes 7 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / j. nagarajan

Actually the question itself is wrong. The rating of
Generators are also mentioned in KVA as both tr. & gen have
a same function of producing apparent power which doesn't
have power factor.

The power factor is a measurement voltage & current utilised
and it will be ratio of apparant power to active power.

But the motors are mentioned in active power as they are
used in various industrial/domestic application utilising
the current & voltage with desired power factor.

Is This Answer Correct ?    0 Yes 6 No

why Transformers power mentioned in KVA?. and why Generators and Motors power mentioned in KW?...

Answer / mani_mc2006

iam not sure. but my answer is Transformer not having load
variation. but Generators and motors having load variation.
so power factor will not be constant. That's why mentioned
like this.

Is This Answer Correct ?    3 Yes 18 No

Post New Answer

More Electrical Engineering Interview Questions

What is method of calculating the fault current for a MDB, 50KW, 3PH, 415V, 50HZ?

0 Answers   L&T,


"TRANSFORMER MODELING AND ANALYSIS" MEANS WHAT AND WHICH TOPICS U READ IN THIS

0 Answers  


i ha done my 10th with 71% ,ITI with 81% 11th with 75% 12th 43% apprentiship with 71% in SAT i secure 1390 ,TOEFL 27 i was refused four times and in all me interview visa officar told that i am not Qualify for study in USA but i completed my 12th yes i got low persentage in my 12th but i seen to much student they already got visa with them 3 or 4 backlocs so why they are refused me ?

0 Answers  


what is mean impedance?

7 Answers   ONGC, Wipro,


transmission line losses

1 Answers   SVS Constructions,


Can we connect two CT'S to one energymeter?

1 Answers   KSEB,


In Energy meter How many rotation Equal to one unit.

3 Answers  


How to check the LM324 Ic

0 Answers  


Single line diagrams for star to delta and DOL starters.

0 Answers  


what happens if dc supply is given to the transformer?

10 Answers  


in what type of applications v can use q meter?

0 Answers  


What is the general system requirement of alternator?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)