Answer / raghavendran
Real power refers to the power that is available to the load
or in other words a power is presently being generated.It
depends upon the load power factor.
Apparent power is the maximum power which, a source is
capable of generating at unity power factor.
for Ex : sqrt3* V*I*COS(phi)keeping v = 20 kv and I=20000A
and COS(phi)= 1
we get Apparent power = 692 MVA
where as for COS(phi)= .85 we get 588 kw which is real power
reactive power is something which is not consumed by the
load.It is available circulating in the grid
always.Depending upon the load connected,it is either
rejected into the grid or absorbed in.
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / bpr
* Real power (P) — watt [W]
* Reactive power (Q) — volt-amperes reactive [var]
* Complex power (S) — volt-ampere [VA]
* Apparent Power (|S|), that is, the absolute value of
complex power S — volt-ampere [VA]
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / asad durez
Real power mean actual power that is equal to
+92-334-9107748
p=vicos@
and it is as known as watt or kilowatt.
and active power mean the rating of a machine.it is equal to
only
VI
and it is as known as VA or KVA
and the Reactive power is equal to
KVAR
mean kilo volt ampere Reactive
KVAR=kva*sin@
| Is This Answer Correct ? | 2 Yes | 9 No |
cable selection formulas for electrical load.
HOW to speed control of induction mototr using scalar control
I have an enquiry of develop solar power plant, 0.69/11kV, 1500kV/750/750kVA, Dy11y11 Transformer. I want to know what does 1500kV/750/750kVA means? Sorry if this is a noob question.
what is the transmission loss for electrical supply? specifically a large shopping complex where the grid is half KM away, what will the % of transmission loss? is there any transmission loss for captive unit generation for above set? thanks
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
What is negative sequence over voltage element?
how to calculate the power factor when instantaneous voltage and current has harmonics in it ?
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
How calculate the Transformer Impedence With Example
How many watts required for single phase power supply?
How to work E.L.C.B and how to connect in circuit.
The Frequency is measured by _________ bridge ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)