For DP type flow transmitter, suppose hp side valve No. 1, LP side Valve No.2, and Equalizer Valve No.1,
Close HP.No.1 Valve
Open Equalizer Valve 3. and then close LP side Valve No. 2
Is This Answer Correct ? | 37 Yes | 10 No |
Answer / mithilesh kumar
i am agree with above answer.
but here on of the important thing that
1st this transmitter is connected in process(DCS) or not,
if connected then 1st this tag must put in CALibration mode.
this facility in YOKOGAWA DCS.
without this action if this tag has been taken in
protection then plant will be trip.
then we can follow above answer.
any comment u most welcome.
good luck
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / sajid
if its a orifice type flow transmitter it must have a 3 way
or way manifold..
in 3 way manifold 2 isolation valve and 1 equlisation valv
will be there..
open the equalisation valve and make sure that DP is 0..
then close low pressure and highpressure valve
Is This Answer Correct ? | 15 Yes | 15 No |
Answer / mohammed abbas
If it is dp type of flow tx,
first if is the 5 way manifold means 2 is isolation
valve,2 is drain valve and 1 is equilizing valve,open the
equilizing valve to make presuure both in HP & LP same and
close the process root valves,then open the darin valves
for flushing it.
Is This Answer Correct ? | 10 Yes | 13 No |
Answer / aswin
First job is to zero check of Tx.
If it will show zero meanns, Tx is ok on its 0 value.
Now u hav to close both isolatoin valve of Tx manifold.
Now open the drain plug of Transmitter.Tx show 0 value.
Next to open drain valave of both H.P AND L.P.(LIR).
The total water will drain out from impulse pipe.
If still u r not getting any flow of water in drain line it means ur lines are severely choked.
After jamming cleared again u hav to charged Tx by some step by step procedure.If condensing pot is there then u v to carefully charge the line.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / abu khaled
1-close the high side valve from manifold
2- open the equalising valve
3- close the low side valve
4- close the equalising valve
5- be careful do not open the three valve in the same time
to avoid damage sensore or cabsoule .sometimes the prosses high temperture or cmical can damege cabsoule>
or maybe there is seale liqude in the high and low side
6- open the vent for low side to zerw check and be sure the equalier valve is closed .
7- if need calibration use high side connections
8- after being sure the TX is oky go to next step
9- make flashing to both sides high and low if they are blugged aske operator to isolate from orfice plate and aske piping group to flash tow lines
10-to return the TX to servse
11- open equalising
12- open the low side
13- close the equalsing
14- open the high side
Is This Answer Correct ? | 8 Yes | 11 No |
Answer / amjad sohail
1. There is no any problem if open the equalizing valve
first. just dp become zero after equalizing valve
opening. so we can open 1st equalizing valve. and
then isolate both process isolation valves at
manifold one by one.
And keep it in your mind at orifice or any other dp
creating device the pressure difference b/w both
sides of transmitter is not high, in fact its a minor
difference b/w both sides.usually minimum 500 ~
2500mmh2o to maximum 10000mmh2o for flow
measurements. and LP side & HP side diaphragms are
designed for bear the same MWP value.(Which is given
at name plate of TX) so there is no matter if high
pressure side process comes to LP side diaphragm. So
if we open equalizing valve 1st then minor difference
of pressure b/w both sides will also become zero.
then we isolate the LP & HP valves one by one.
2. If we 1st isolate high pressure side of tx then pressure will be trapped B/W transmitter and isolation valve of manifold. so there is no any problem if we isolate the high pressure side 1st. (But do not open the drain of HP side. Because its very harmful for TX due to transmitter will come to its maximum & out of range dp value before isolate the LP side and open the equalizing valve.) So do not operate the drain valve and open the equalizing valve & then isolate the low pressure side. Now we can drain the LP & HP side respectively. And usually this practice is adopted by all instrument technician and engineers.
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / suresh agravat
First close root valve
second isolate manifold valve
open equaliser valve it was zero check procedure
open root valve
open manifold isolated valve
close equaliser valve it was taken in line procedure.
Is This Answer Correct ? | 0 Yes | 8 No |
What is DCS and PLC scanning time?
what is DCS?
Explain the working of rota meter.
How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer.
My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
What is an analog input - output , digital input - output . Any example ???? How they r known its ai-ao or di - do
1- Explain about HPM 2- What is the FSC and explain the configuration of FSC 3- explain the complete loop of vibration, how it works (field to control room) 4- What is the use of proxymitter? 5- During job your partner effected with H2S then what you have to do. 6- what type of gland packing uses when valve glind is leaking.
modbus and profibus communication difference?
what is temperature compensation?
Sir , i have completed my M.Sc In Instrumentation and presently working in Maintenance department 3 yrs Exp , is there is any possible for work in offshore ..
How does pyrometer works?
regarding level tx i would like to know how to select the range of the level transmitter in a closed drum(steam drum or deaerator)?