Answer / mrmk
Dear Brother Ali,
Can you provide us whether you going to calibrate Analog
transmitter or SMART transmitter?
If Analog transmitter means No way
If SMART means you can change your LRV and URV online.It
doesn't mean full calibration but it will adjust the
transmitter output according to LRV/URV
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ali
dear brother i need correct procedure in detail my question is . HOW CALIBRATE TRANSMITTER IN ONLINE (RUNING PLANT)I MEAN WE DO NOT ISOLATE TRANSMITTER OR SHOULD ISOLATE IT THEN NEXT SHOULD I CHANGE IN CONTROLLER OR DCS SYS. WHAT TO DO.??
| Is This Answer Correct ? | 0 Yes | 0 No |
First tx.put force condition or manual mode in the dcs.after that the start calibration procedure in the field.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / debyendu
we can calibrate transmitter with a hart communicater which
is to be connected with 250 ohm resistance in series with
transmitter to the power supply unit.
| Is This Answer Correct ? | 4 Yes | 5 No |
How to measure Flow of air line,what is the procedure of creating DP in line to measure Flow!
Range 8 Kg/cm2, alarm to be set at 2Kg/cm2, at wat pressure reciever switch to be calibrated? justify the ans?
Where can i take training in intools software for Instrumentation design??
How we calculate orifice plat size???
what is piezo electric transducer?its principle?
I will attend an interview with GasGas company for a position of Instrument Technician ( Offshore )in next month can anyone tell me what questions they will ask. Thanks in advance.
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
what is radar type level transmitters and its basic principle and how to calibrate it
What is flow ,level, pressure transmitter ?and units?
What is motion balance principle?
It is desired to reduce effect of 50Hz pick up in a thermocouple measurement. If a third order LP filter is used for this, what should be its cut off frequency, if gain should be 0.001 at 50Hz.
Please why do we use 4-20ma in instrumentation engineering
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)