how to connect generators in parallel and what are the
required equipment to do so?
Answers were Sorted based on User's Feedback
Answer / paramesh
for the two generators connected in parallel by following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,synchronuscope will be
used.
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / bijulal
for the two generators connected in parallel the following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,wattmeter,
synchronuscope& reverse current relay will be
used.
| Is This Answer Correct ? | 10 Yes | 3 No |
Shall we get electrical shock if we touch the positive terminal of a 230 volt dc supply?
During Load testing of battery charger with temporary AC Generator .When reach 70% load Generator immediately shutdown .we could not able to Recognize ,what is exactly problem .Please kindly clarify us
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
what is the difference between effective earthing and resistive earthing?
what is means of ALF,kPV(min),lexc(max)at Vk,Rct@75 degree centrigate ohm in current transformer name plate?
If load current is 70amps or 50amps what range of CT to install for ampere metering
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
If an induction motor is restarted before its rotor stop rotating, then what will be the amount of current drawn? Is this current will be the same as motor starting current?
For some transformers we are using solid neutral earthing while some others we are using resistance earthing why ?
what is MUSS?
What is the maximun current carring capacity in per phase for three pole 100anps rating ncb
Whata are the types of Cables?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)