Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


During he starting up of the motor, the upstream's MCCB
(350A) always trips due to the UVT relay activated.
Can Star-delta starter use for a 20kW Motor (For a powder
mixer machine) cause voltage-dip in the supply line voltage?
If so, what are the recommended solution to
eliminate/reduce the transient voltage dip in the line
voltage?

Answers were Sorted based on User's Feedback



During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT re..

Answer / tushar patil

yes u can use star delta starter
20KW means 30HP motor
u can use VFD (variable frequency drive) also
it is very easy to u
if cable length is more than 50 m then u should connect output line chock to output n input line also connect line chock..
n increase accelaration time in vfd

Is This Answer Correct ?    0 Yes 0 No

During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT re..

Answer / piyush rana

You can check the length of the cable from the supply to
motor, I think It will be more so that due to line
resistance loss during starting the line voltage will go
down for the fraction of seconds.
please mention the connected load, transformer capacity,
volatge incoming etc for further clear answer.

Is This Answer Correct ?    0 Yes 1 No

During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT re..

Answer / abdulsubur

up to 3kw Dol startor
up to 7kw we can use Star delta startor

Is This Answer Correct ?    2 Yes 3 No

During he starting up of the motor, the upstream's MCCB (350A) always trips due to the UVT re..

Answer / abdulsubur

upto 35kw motor u can use star delta

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

The unit of quantity of electricity is the:(a) volt(b) coulomb(c) ohm(d) joule

1 Answers  


A ray hit a smooth regular surface at an angle of 20 from the normal. Calculate : 1. The angle btw the incident and reflection ray. 2. The angle of deviation.

0 Answers  


why using touble tube lamp use in factory?

3 Answers   ONGC,


is the secondary voltage of current transformer greater than primary voltage,,,,,,,,] give the example with ct burden,current ratio,and primary and secondary side voltage?

2 Answers  


what is a motor

5 Answers   Eskom,


Why transformer used in UPS??

0 Answers   JLL,


3 pahase 750kva Running 2 DG sets in 35 mints.525ampers. and 616 kw how much fuel consumption in Generator.what is the formula.

1 Answers   Delite Systems Engineering,


i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.

0 Answers   Bay Fishing Corporation,


when a 500kva-400hz single phase transformer operated on a 100hz supply then what will be kva required

2 Answers  


hello friend i wish to study a course related to the electrical construction, controlling and monitoring , which course i want to study? pls give me the name of institute?

0 Answers  


What is turn ratio of a transformer?

0 Answers  


Can Anyone Answer anyone of these ? Q1) why direct SOLUTION of Load Flow Studies in Not Possile ? Q2)Why majority of Buses in power system are load buses Q3)Why one of the buses in Power system is taken as reference bus (slack or swing) Bus ? Q4)Bus Admittance Matrix is a sparce (means it contains some zero elements ) matrix , give reason

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)