During he starting up of the motor, the upstream's MCCB
(350A) always trips due to the UVT relay activated.
Can Star-delta starter use for a 20kW Motor (For a powder
mixer machine) cause voltage-dip in the supply line voltage?
If so, what are the recommended solution to
eliminate/reduce the transient voltage dip in the line
voltage?
Answers were Sorted based on User's Feedback
Answer / tushar patil
yes u can use star delta starter
20KW means 30HP motor
u can use VFD (variable frequency drive) also
it is very easy to u
if cable length is more than 50 m then u should connect output line chock to output n input line also connect line chock..
n increase accelaration time in vfd
| Is This Answer Correct ? | 0 Yes | 0 No |
You can check the length of the cable from the supply to
motor, I think It will be more so that due to line
resistance loss during starting the line voltage will go
down for the fraction of seconds.
please mention the connected load, transformer capacity,
volatge incoming etc for further clear answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / abdulsubur
up to 3kw Dol startor
up to 7kw we can use Star delta startor
| Is This Answer Correct ? | 2 Yes | 3 No |
what is rotatng magnetic field in case of three or multiple phase alternating current machines???
The control system is used for?
Air refrigeration cycle works on the
why we +ve load distribution in 24v and -ve load distribution in 48volt in the telecom sector.?
what is the chiller and working principal
what is the burden?accuracy?Knee point voltage? what is the Alternator of PGM?
in alternator what is use of AVR ? how AVR is operating either AC or DC?
can we use existing 6300V alternator for generating 6600V by increasing excitation,what are advantages & disadvantages to alternator & motors of 6600V.
What are the various types of BUSBAR Schemes? explain each
why current flow to the opposite direction of flow of electrons???????????
How much resistance between neutral earthing and body earthing of Power transformer?
why slipring motor , at full speed run as squirrel cage motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)