During he starting up of the motor, the upstream's MCCB
(350A) always trips due to the UVT relay activated.
Can Star-delta starter use for a 20kW Motor (For a powder
mixer machine) cause voltage-dip in the supply line voltage?
If so, what are the recommended solution to
eliminate/reduce the transient voltage dip in the line
voltage?
Answers were Sorted based on User's Feedback
Answer / tushar patil
yes u can use star delta starter
20KW means 30HP motor
u can use VFD (variable frequency drive) also
it is very easy to u
if cable length is more than 50 m then u should connect output line chock to output n input line also connect line chock..
n increase accelaration time in vfd
| Is This Answer Correct ? | 0 Yes | 0 No |
You can check the length of the cable from the supply to
motor, I think It will be more so that due to line
resistance loss during starting the line voltage will go
down for the fraction of seconds.
please mention the connected load, transformer capacity,
volatge incoming etc for further clear answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / abdulsubur
up to 3kw Dol startor
up to 7kw we can use Star delta startor
| Is This Answer Correct ? | 2 Yes | 3 No |
How to know motor winding is star or delta connected without see the information table and winding connection ?
Technical specification of a wind farm
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
IN A HT CABLES i.e. 1.9/3/3 kv, what is the meaning of 1.9 and 3.3.
In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?
What is meant by directional power and reverse power relay ?
what happens when we apply dc to a transformer
what is V0/V rating of cable
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
what will happen when excitation of a synchronous machine is suddenly reduce to zero when it is running at full load..??
Our transformer capacity is 500kva & voltage ratio is 11kv/433v step down tf.Now i need to know if my input voltage is 10500v and what would be the secondary side voltage i.e output voltage ?
why dc series motor high speed motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)