Answer / habib
Cable size (sq.mm.) is selected dpendent on 4 facors
1. Current carrying capacity (popularly termed Amapcity)
of the cable.
2. Voltage drop that can be tolerated at the load point.
3. Short circuit tolerance of the cable.
4. Mechanical strength of the cable.
A cable is selected fo the job that can meet all these
criteria.
Basically HT and LT cables are of same material but the
difference is in insulation.
Looks too much like a text book lesson. If you can post
your exact requirement, I would try to help.
| Is This Answer Correct ? | 4 Yes | 2 No |
For refrigerators the motor current is raised beyond its rating on both conditions when the voltage of the system is more(say 270v) than the rated voltage(220v) as well as when the voltage of system is less(say 160v) than normal voltageof 220v, why explain?
0 Answers Electrical Tech, UPSE,
what is settable hystersis protection? If any body knows plz kindly post the answer..
campared to ac, in dc corona loss is
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what is the use of cable in our environment ?
what is the CT & PT. where is it uses.what is the using that plese kindly answer me...?
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
AC covered area by ton calculation
why we use 6nos of C.Ts on 11kv incoming?
WHAT INSTRUMENT IS USED TO MEASURE THE MAGNETIC FLUX?
y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..
how to calculate mf when meter and cTPT detail are given
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)