We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Disconnect earth and measure voltages between phases and
neutral on some load.If the voltages are not equal there is
a loose connection in the star point.Before doing
this ,check the earth connection at neutral bushing.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya199307@gmail.com
Such types of problem occur due to increased in value of earth pit.
So 1st you checked the all earth pit values individually by opening all the grounded connections.
As per standard the values of earthing in HT yard should be less than 5volt.
If the value is greater than 5 volt then apply the procedure to reduce the value, which is different as per type of earthing (Normal or Chemical).
If the values should be comes as per rated value your problem is short outed.
If you talking theoretical part then voltage between N & E is zero.
But practically 2 volt is permissible but i.e. also not good for the system
It will affected on electronics system.
Such types of problem occur in the hilly areas or in rocky soil.
( If the value will not coming as per standard then add n....number of earth pits in series otherwise use counterpoise method.)
| Is This Answer Correct ? | 0 Yes | 0 No |
how to get electrical supervisor competency certificate in gujarat. i did 3 year diploma in electrical
What is the formula for calculating Transformer Losses & Efficiency. I want to compare the Transformer efficiency at different loading condition.
6 Answers Rays Power Experts, Techser,
Define phase cross over?
Please let me know DG set b check how many hour and days.
if we convert kw into Ampers,which one formula use by us,pls tell me?
can i use 4 number of circuit breaker as single phase manual change over switch? if yes then how plz also send ckt diagram at nazimzamurad@gmail.com
Why red,yellow,green colours lamps are used in the traffic control?
What is contract demand in solar system?
What should be the length of transmission line so that we can see/obtain the full sine wave of voltage??
For a 500 MVA 400/220/33KV transformer following data given HV power = 500 MVA IV power = 500 MVA LV power = 5 MVA If input power is 500 MVA then how output power is (500+5)MVA. Can anyone help
what is neutral voltage
does magnetic interlocking take place in an induction motor ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)