We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Disconnect earth and measure voltages between phases and
neutral on some load.If the voltages are not equal there is
a loose connection in the star point.Before doing
this ,check the earth connection at neutral bushing.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya199307@gmail.com
Such types of problem occur due to increased in value of earth pit.
So 1st you checked the all earth pit values individually by opening all the grounded connections.
As per standard the values of earthing in HT yard should be less than 5volt.
If the value is greater than 5 volt then apply the procedure to reduce the value, which is different as per type of earthing (Normal or Chemical).
If the values should be comes as per rated value your problem is short outed.
If you talking theoretical part then voltage between N & E is zero.
But practically 2 volt is permissible but i.e. also not good for the system
It will affected on electronics system.
Such types of problem occur in the hilly areas or in rocky soil.
( If the value will not coming as per standard then add n....number of earth pits in series otherwise use counterpoise method.)
| Is This Answer Correct ? | 0 Yes | 0 No |
Where the Dry type tranformers are used.
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??
how to connect generators in parallel and what are the required equipment to do so?
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
what is purpose of using neutral grounding transformer in generators??
WHY TRANSFORMER IS MEASURED IN KVA?
what is meant by neutral Ct of a transformer and how it connected in transformer
what is a starter ??
please suggest some good universities with low cost iam in totally full confusion so please help me my profile gre 283 and ielts 5.5
Does human body can effect the electric shock when stand on Insulated material?
3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442
why ct is connected at bushing of transformer ??????????
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)