We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Disconnect earth and measure voltages between phases and
neutral on some load.If the voltages are not equal there is
a loose connection in the star point.Before doing
this ,check the earth connection at neutral bushing.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aditya199307@gmail.com
Such types of problem occur due to increased in value of earth pit.
So 1st you checked the all earth pit values individually by opening all the grounded connections.
As per standard the values of earthing in HT yard should be less than 5volt.
If the value is greater than 5 volt then apply the procedure to reduce the value, which is different as per type of earthing (Normal or Chemical).
If the values should be comes as per rated value your problem is short outed.
If you talking theoretical part then voltage between N & E is zero.
But practically 2 volt is permissible but i.e. also not good for the system
It will affected on electronics system.
Such types of problem occur in the hilly areas or in rocky soil.
( If the value will not coming as per standard then add n....number of earth pits in series otherwise use counterpoise method.)
| Is This Answer Correct ? | 0 Yes | 0 No |
any earth foult trip the relay but in welding time not trip by earth foult
0 Answers Power Grid, Siemens,
Air refrigeration cycle works on the
can anyone tell me the website for star-delta control diagram?
which fault current is maximum: 3 phase short circuit, LG, LL or LLG?? why?? in one of the problems that i have solved, 3 phase short circuit current on an unloaded generator came out to be less than the LG fault current. can anybody please explain why.
How to decide whether A / B / C / D curve type MCB should be used?
What is the meaning of In,Io & Ir in Circuit breaker? How to calculate?
if 2500 KVA TRANSFORMER CAPACITY.33KV INCOMING HOW ARE AMPEAR PRIMERY SAID
which type of breaker sould be used for different level of voltage ? (i.e at 11 Kv, 33 Kv, 66 Kv....
Sir, I need a power supply at 380V. The supply I get in three phase is rated 415V. The total supply I have from the supply company is 70KW. Kindly inform if it is better to use a voltage stabiliser for this purpose or a transformer
What is transister define the transister ammiter ,base, colector.
What is the drawback of class b amplifier? How is this minimized?
why r we using vaccuum circuit breakers in the place of m.o.c.b.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)