We in my plant one of the transformer showing neutral to
earth voltage is 22V how to solve it
Answer Posted / wasim
Check resistance of earth pit/mesh connected with Start
point (Neutral of Transformer). If reisitance is more than
5 Ohms your Neutral to earth voltage will be increased
accordingly. So you have to improve the resitance of your
earthing network to less than 1 Ohm
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
can indirect loading be called as phantom loading?
What are the causes of having an rmu explode after installation? And how do u treat the bushings of an rmu?
What is the current carrying capacity of 35sq.mm flexible cable?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
I am experienced with house and industrial wiring but I don't have any licence how can I apply an licence and which type of licence i can get i didn't complete deee just only experience
what is the power rating of CPU, CRT type moniter, LCD type moniter,scanner Approx.
from which formula we select a capacitor rating?
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
What happen when change order of CT in GIS feeder?
what would happen if reactive power (kvar)is increased (more)or decreased (less)? how much exact reactive power should be maintained? and what should be done for that
which connection is safer series or parallel?usually which connection we prefer at home?
We have studied about many techniques for finding the stability of system, ROOT LOCUS, ROUTH, BODE PLOT, POLER PLOT etc. In these which is used where. what are the difference among them... PLZ tell me.......
hi pal, i am vengatesh from tamilnadu(chidambaram),i have called for the written test for the post of jr executive(ELECTRICAL) of AAI ,I dont know about the question paper pattern,so any kindly help me to face the examination,post me the model question papers and some tips to write my examination to (vengi.annadurai@gmail.com)
how to calculate insulation level of transformer?
EXPLAIN WHY THE SURGE CURRENT RATING OF AN MCCB OR CIRCUIT BREAKER DECREASES WITH INCREASE IN THE RATING OF MCCB OR CIRCUIT BREAKER.