if 2500 KVA TRANSFORMER CAPACITY.33KV INCOMING HOW ARE
AMPEAR PRIMERY SAID
Answers were Sorted based on User's Feedback
Formula is KVA/ 1.732* volt
2500*1000/1.732*33*1000
2500/1.732*33
43.73A
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prem
in this question is wrong because whether transformer is
delta to star or star to delta
step1 if transfomer is delta to star fourmela is
kv/volt answer is 75.75amps
step2 if star to delta fourmela is kv/volt*1.732
answer is 43.73amps
Is This Answer Correct ? | 3 Yes | 0 No |
SUPPOSE A CIRCUIT BREAKER HAS TRIPPED THE THE LINE WHEN A FAULT OCCUR ON IT.NOW WHEN THE FAULT HAS BEEN CLEARED, HOW THE CIRCUIT BREAKER WILL CLOSE AUTOMATICALLY NOT MANUALLY.
6 Answers Bureau of Energy Efficiency, DVC,
why some time Railway Fan not Rotate,But after a small rotation by human then it rotate normally? Why?
Write the programming software name for LG, SIEMENS,Messung,AB
Is there any specialised book to refer about fault level calculation both in MV and LV side??
How many input terminal of single phase transformer.which is use for rural power distribution.
Can motor act as generator (OR) vice versa? explain how does it do please post the answer technically
what is die electric strnth of transformer ?
a battery is having capacity 100AH and 25% charging .if a load taking 10A & connected 6 hour .what is the final condition of the battery.
how we are measuring the import and export power?
why dc did not flows to earth?
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
A synchronous motor is operating at a leading power factor .if the applied voltage is decreases ,(the excitation remains constant ) ,the motor current a)increases b) decreases c)remains same d) none of these