which fault current is maximum: 3 phase short circuit, LG,
LL or LLG?? why??
in one of the problems that i have solved, 3 phase short
circuit current on an unloaded generator came out to be
less than the LG fault current. can anybody please explain
why.
Answers were Sorted based on User's Feedback
Answer / shubham gupta
it depends upon the grounding method employed.
LG fault current is more if the generator is solidly grounded.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dr rajan
It is always the 3 phase bolted fault. Check your problem
again. You may have made a mistake. Why 3Ph fault current is
high?
When all phases are grounded or shorted, the impedance is just
let us say X in each phase leading to V/X x 3 times. where as
when you have LG, you will include the line impedance in
series with X, equals X+xL, which is more than X on 3Ph short
ckt. When you divide V/(X+xL) what will you have???? More
current or less current???????
Is This Answer Correct ? | 1 Yes | 2 No |
how to check avr of dg set of 125kva
why indicated sypply only by 440V in 3-phase system.
why transformer ratings in kva?
99 Answers Bhel, College School Exams Tests, DOW, Emco, Esab, GE, KCP, PGCVL, Sodexo, TCS, vtps, Wipro,
What are the advantages of D.O.L Starter in 3 phase induction motor?
One Township having 850 house and each house load is 2.2KW single phase & 5HP 3 Phase motors of 10 Nos .Who can calculate 11 KV transformer capacity .dilip_bhasker@yahoo.co.in
what is the use of interposed & reverse voltage transformer
what are the values of VRY,VYB,VBR,Vry,Vyb,Vbr,Vrn,Vyn,Vbn for Magenetic balance test of 100 KVA and 63 KVA Distribution transformer
Which is stiffer between salient pole rotor and cylindrical rotor synchronous machines? Justify your answer.
what is the difference between Current transformer & Capacitive voltage transformer
how nautral is provided for return path is 3 phase induction motor
what will be the neutral to earth voltage while checking by the Digital multimete? and why?
What is the basic principle of operation of alternators/dc generators?