what is the conductor size in 33/11 kv line
Answers were Sorted based on User's Feedback
Answer / aajinkya
Generally 300 square mm conductor is used in case of 33kv line
Is This Answer Correct ? | 21 Yes | 8 No |
Answer / ajit g. k.
How can you find out the cable size without knowing the
load requirements, the current that is to flow through it.
And also, a line can never be 33kV and 11kV at the same
time. A 11kV line becomes a 33kV line when it passes
through a transformer(just for info). The cable sizes
differ as the current flow is different.even the conductors
change. In transmission lines that carry current say, 1000A
in 11 kV, its about 334A in 33kV line which follows. The
cable used is XLPE in 11kV and in 33kV we use AAA
conductors. sizes stil depend on many other factors too.
Is This Answer Correct ? | 14 Yes | 9 No |
can we synchronize star system generators with delta system transmission line ? and how ?
15 kva dg set single phase takes 63amp( approximate) while same rating 15kva three phase takes 35amp approximate. why ? and what will be per phase current for 15 kva
how to give earthing in plain?
what is the highest transmission voltage in India till now?
Generation of voltage for each phase are same of a turbogenerator.Although the short circuit current flow when two phase of turbogenerator are shorted(where current can't flow without potential difference),why?
What is the lower limit of megger value for 66/11KV power Transformer ?
7 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd, Torrent Power,
In a generator (Synchronous) does the rotor speed (frequency) corresponds to the speed of the water (in hydro). does the torque on the turbine relate to the flow of water?
Hello sir, pls send me hpcl technical test papers .i am. Appearing for the exam.
generaly all power generating devices is expressed in KVA or MVA then why power ststion is expressed in MW
Write down the brushes of a de machine.
WILL SCHNEIDER MAKE ACB(MASTERPACT)TRIP ON REVERSE POWER?
why auto transformer connected in star?