Three phase alternators are connected in star connection
why?
Answers were Sorted based on User's Feedback
Answer / ashna & anju
in star conection ,phase voltage is lesser than line
voltage and induced emf in the phase winding of an
alternator is directly propotional to number of turns,a
star connected alternator will require less number of turns
than a delta connected one for the same line voltage.
Is This Answer Correct ? | 68 Yes | 10 No |
Answer / $$$
TTT
IT IS BECAUSE THIRD HARMONICS CAN BE ELIMINATED USING STAR
CONNECTION AND DISTRIBUTED WINDINGS IN 3-PH ALTERNATORS..
Is This Answer Correct ? | 36 Yes | 14 No |
Answer / ajay
IT IS BECAUSE THIRD HARMONICS CAN BE ELIMINATED USING STAR
CONNECTION AND DISTRIBUTED WINDINGS IN 3-PH ALTERNATORS..
Is This Answer Correct ? | 17 Yes | 5 No |
Answer / muhammed konikkal
out put is required in AC form with neutral.Neutral can be taken only from Star connection. We can take out put single phase or three phase depending our load.
Is This Answer Correct ? | 8 Yes | 7 No |
in a star connection, phase voltage Vph = VL/ (3)^1/2.
1--Since the induced emf in the primary winding of an alternator is directly proportional to the number of turns, a star connected alternator will require less number of turns than a delta connected alternator for the same voltage.
2-- it also requires less insulation bcz its phase is less.
3-- it also help to reduce third harmonic ...
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / sudheer
induce emf is proportional to turns so for same line voltage no of turns required is less hence insulation required is less and for protectio purpose we require ground so ground provided in case of star only
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / binod pradhan
2-in star connection the phase voltage is low than the line voltage,so it required less no of turn. 3-low insulation required as phase voltage is low. 4-1 neutral point available in star connection. 5-unbalance current flowing in the three phase circuit, neutral is having a vital role.It will take the unbalance current through to the ground.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mahfooz alam
In Star connection the Line Voltage is 1.732 times the phase voltage. As a result of which we can have the higher voltage in star connection when compared to the delta connection. Thus, to have more output voltage Star connected Alternator are used.
Is This Answer Correct ? | 6 Yes | 12 No |
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
why voltage rating of transformers are in multiples of 1.1?
sir what is the purpose of SF6 in HT breaker and what is the pressure should be maintain in the breaker?
why co incidence factor considered in transformer sizing?
ALL HT /LT PANEL TEST? DISCRIPTION.
What is the difference between a Vacuum Circuit Breaker and a Load Break Switch?
In 11kv transmission line whats the maximum power can be drawn?
What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)
17 Answers Alstom, Call Centre, EDC, HCL, Procon Engineers,
What is the complete procedure of erection of electrical panel in industry
what is the IS foe lightning arrester?
Why is it not possible to operate a star-delta transformer in parallel with delta-delta transformer?
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
0 Answers Anglo Platinum, Narnarayan Electrical,