Can CT Secondary left open circuited and why(reason)?
Answers were Sorted based on User's Feedback
Answer / jayakumar.k
CT Secondary should never let open condition. Since there
is no opposing flux in secondary circuit Primary flux will
develop enormously high that would cause bursting of CT and
also damage to the person who is working with it.( Remember
induction principle)
| Is This Answer Correct ? | 26 Yes | 0 No |
Answer / raul
absolutely NOT bcoz during normal operating conditions, the
primary and secondary current are equal and opposite to
each other.........so the mmf of both primary and secondary
are in direct opposition........but secondary current is a
bit lesser than d primary current and this difference is
utilised in magnetising the core.......but if the secondary
is left opened then there will be no demagnetising mmf left
and excessive flux will b generated in the core and due to
this enourmous amount of voltage will b produced in the
secondary which is very harmful for life and CT also. also
there will be a loss of accuracy in future due to residual
flux left in the core.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / muhammad nazim
A CT is basically a step-up transformer(from voltage point
of view).In the case of 400/1 A CT the primary turn is 1
(say the busbar)and the secondary turns is 400.How much
will be the primary voltage drop?? it will be in millivolts
for a busbar.So this millivolts multiplied by 400 will
cause just around a few volts (say 3 to 10V) for an open
secondary.But i have read that the secondary voltage will
reach a few kilovolts for a 400/1A CT at full load
conditions.My question is how it will reach a few kilovolts
and damage the CT on open secondary condition?As we have
seen above the max voltage wil be just in few volts.So
please someone
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / bharat sharma
Let us assume we have 600 V and 200 A on primary side of the
CT. Ct ratio is 200:1 In that case Secondary voltage would
be (600V x 200A)/1A = 120000 V. Would you like to leave
120000 V open circuit irrespective of current capacity of
secondary circuit?
| Is This Answer Correct ? | 8 Yes | 10 No |
what is protection class current transformer.
which pole motor is best ?4 pole motor or 6 pole motor,why?
whata is battery charger ?how many cells connected for 110v?
What is the earth treantment procedure?
Why we use RYB phase sequence?
if i conncet ct with ct ratio of 600/5 to an energy meter having ct ratio of 100/5, the reading show by the meter will correct, if wrong is there any method to calculate correct value with shown value, if yes please state it.....
what is the saturation point of crgo lamination.
what are the specifications for Dc cables of higher rating
how we select the fuse and OLR rating for 3 phase induction motor from 1HP TO 100 HP?
after parallaing two generators current is shooting up in both the generators.for ex: load is 400 kw..after paralling and load sharing current in running gen is approx 900 amps and incoming is 750 amps which is too high when trying toshift the load current in incoming gen is coming more than 1300 amps and both getting tripped and making blackout..
Does voltage and current can be seperated?
in the Distribution system .which one is Most Economically used by Power Engineer ? a)3 Phase3 wire System or b) 3Phase -4wire System
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)