how to calibrate temprature switch and flow switch ?
Answer / carl_ellis
The key to 'calibrating' a temperature switch is it is a
switch, it is not a continuous analog sensor. So there's
no need to mess around with a zero and span value, like you
would on temperature transmitter.
All that matters is setting the switch's trip point, the
setpoint, and in some cases, the reset
(deadband/hysteresis) point. There is no need to mess
around anything but the trip point, it's time consuming
enough to get a precise setpoint on switch.
You need to know
- the setpoint
- in some cases, the reset (deadband/hysteresis) point
values
- whether the setpoint (SP) is for a rising or falling
temperature. Because they're mechanical switches, a SP for
falling is NOT same as a SP for rising.
- switch functionality - Does the switch close or open on
rise or fall. There are applications for all the
variations: close on rise, close on fall, open on rise,
open on fall.
Check how to change the setpoint on the switch. Some
switches have a setpoint lock (nut). Some are blind
adjustments, some are adjustments with indicated
temperature values. Some have a separate
deadband/hysteresis adjustment. The latest temperature
switches are digital, and the setpoint and hysteresis reset
point are entered as values.
Many procedures require an actual test with a calibrating
heat/cold (dry block calibrator or oil bath) source and a
temperature "standard" is needed for a reference
temperature, to prove the mechanical setting is correct.
Sometimes the standard is a certified dry block with a
readout, sometimes it's a mercury thermometer, sometimes
its certified RTD with a certified readout. Older cal
equipment has stand-alone electrical equipment, like an
indicator lamp or an ohmmeter that is used to indicate
switch closure on the temp switch, more modern cal
equipment has built-in connections and an indicator for
that.
Make the setpoint adjustment, run the temperature source,
heat or cool, and note the trip and reset points. If
needed, make adjustments and re-run the test until the
setpoint (and reset point) are within the spec needed.
Record the results, put a cal sticker or tag on the beast,
and you're on to the next one.
Tell 'em Carl sent you.
Is This Answer Correct ? | 8 Yes | 1 No |
how feedback signal frm rtd can be use for 2 purpose, i.e. 1for local monitoring and 2nd for controlling in dcs.so how many wired RTD can be used
how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?
What are different types of orifice plates?
If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.
1 Answers Process Control Technologies,
what is the working principle of hydra step(electronic level indicator)?
2 Answers Bengal Energy, Lanco,
what is the difference betwwen the 2wire level transmitter and 4wire level transmitter??and their applications also??
What is the main difference between the terms instrumentation and Automation?
Where do we consider the pressure in mbar & where do we consider the pressure in bar & why is it so ?
2 Answers BOC, Jindal Steel and Power,
what is meant by calibration
What is the difference between HMI and MMI?
I need the intools training institute address in india. Intools subject oriented local authors books.Refer me plz
GIVE BRIEF DESCRIPTION ABOUT "DCS"