how to calibrate temprature switch and flow switch ?
Answer / carl_ellis
The key to 'calibrating' a temperature switch is it is a
switch, it is not a continuous analog sensor. So there's
no need to mess around with a zero and span value, like you
would on temperature transmitter.
All that matters is setting the switch's trip point, the
setpoint, and in some cases, the reset
(deadband/hysteresis) point. There is no need to mess
around anything but the trip point, it's time consuming
enough to get a precise setpoint on switch.
You need to know
- the setpoint
- in some cases, the reset (deadband/hysteresis) point
values
- whether the setpoint (SP) is for a rising or falling
temperature. Because they're mechanical switches, a SP for
falling is NOT same as a SP for rising.
- switch functionality - Does the switch close or open on
rise or fall. There are applications for all the
variations: close on rise, close on fall, open on rise,
open on fall.
Check how to change the setpoint on the switch. Some
switches have a setpoint lock (nut). Some are blind
adjustments, some are adjustments with indicated
temperature values. Some have a separate
deadband/hysteresis adjustment. The latest temperature
switches are digital, and the setpoint and hysteresis reset
point are entered as values.
Many procedures require an actual test with a calibrating
heat/cold (dry block calibrator or oil bath) source and a
temperature "standard" is needed for a reference
temperature, to prove the mechanical setting is correct.
Sometimes the standard is a certified dry block with a
readout, sometimes it's a mercury thermometer, sometimes
its certified RTD with a certified readout. Older cal
equipment has stand-alone electrical equipment, like an
indicator lamp or an ohmmeter that is used to indicate
switch closure on the temp switch, more modern cal
equipment has built-in connections and an indicator for
that.
Make the setpoint adjustment, run the temperature source,
heat or cool, and note the trip and reset points. If
needed, make adjustments and re-run the test until the
setpoint (and reset point) are within the spec needed.
Record the results, put a cal sticker or tag on the beast,
and you're on to the next one.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 8 Yes | 1 No |
What is basic of instrumentation
what is the difference between hub and switch?
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
WHY THE DEGREE OF VALVE PLUG AND VALVE SEAT IS SLIGTLY DIFFERENT I CONTROL VALVE TRIM DESIGN
what is meaning of software redundency and hardware redundency?
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
which type signal come control valve
what is the procedure of O2 sensor(ABB) calibration?
What is pressure,What is temperature,What is flow,What is level
What is ALSPA 370 control system
1 Answers DUBAL-Dubai Aluminium,
how to adjust relay in smart positioner ?
hii my name is sujith...i am preparing for HPVL GET 2010... so ,,,pls help me by send any previous questions or material to my site.....(Msujith_12@in.com) thank q
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)