how to calibrate temprature switch and flow switch ?
Answer / carl_ellis
The key to 'calibrating' a temperature switch is it is a
switch, it is not a continuous analog sensor. So there's
no need to mess around with a zero and span value, like you
would on temperature transmitter.
All that matters is setting the switch's trip point, the
setpoint, and in some cases, the reset
(deadband/hysteresis) point. There is no need to mess
around anything but the trip point, it's time consuming
enough to get a precise setpoint on switch.
You need to know
- the setpoint
- in some cases, the reset (deadband/hysteresis) point
values
- whether the setpoint (SP) is for a rising or falling
temperature. Because they're mechanical switches, a SP for
falling is NOT same as a SP for rising.
- switch functionality - Does the switch close or open on
rise or fall. There are applications for all the
variations: close on rise, close on fall, open on rise,
open on fall.
Check how to change the setpoint on the switch. Some
switches have a setpoint lock (nut). Some are blind
adjustments, some are adjustments with indicated
temperature values. Some have a separate
deadband/hysteresis adjustment. The latest temperature
switches are digital, and the setpoint and hysteresis reset
point are entered as values.
Many procedures require an actual test with a calibrating
heat/cold (dry block calibrator or oil bath) source and a
temperature "standard" is needed for a reference
temperature, to prove the mechanical setting is correct.
Sometimes the standard is a certified dry block with a
readout, sometimes it's a mercury thermometer, sometimes
its certified RTD with a certified readout. Older cal
equipment has stand-alone electrical equipment, like an
indicator lamp or an ohmmeter that is used to indicate
switch closure on the temp switch, more modern cal
equipment has built-in connections and an indicator for
that.
Make the setpoint adjustment, run the temperature source,
heat or cool, and note the trip and reset points. If
needed, make adjustments and re-run the test until the
setpoint (and reset point) are within the spec needed.
Record the results, put a cal sticker or tag on the beast,
and you're on to the next one.
Tell 'em Carl sent you.
| Is This Answer Correct ? | 8 Yes | 1 No |
Is Hart communicator calibration device or communicating device for transmitter?
what is controlling card in dcs? how u measure dcs memory?what is bus in dcs?how u know dcs speed n ehternet speed?
1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling
what is the diffrene between DCS System and PLC System
generally for transmitter we are giving supply 24vlts?but we are getting output 4-20ma ? how it is possible? is there any operation inside the tx?pls give complete information?
What is the processor scan time of allen bradle control logix processor 5555 lenin lenin123us@rediff.com
What is seismic transducer?Where it is used?
My question may be very basic or childish but this question still persists in me, someone plz help me 1.why do we go for differential equations to analyze a system? 2.why do we solve it using matrices, is there any specific reason for using matrices other than the stories like it is simple,faster etc.
how to calibate level transmiter ?range -150 to +150.what is the zero and span?
what u mean by speed control in turbin? how it was working?
What is the difference between working pressure and calibration pressure of a control valve
pls any1 sugges me book for plc,dcs & scada..
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)