Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Actually why the transformers are rated in KVA.?

Answers were Sorted based on User's Feedback



Actually why the transformers are rated in KVA.?..

Answer / pradyumna171

Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the
real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO KNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply.

PRADYUMNA CHANDRA PANDA
Mob No- 9439721208

Is This Answer Correct ?    8 Yes 0 No

Actually why the transformers are rated in KVA.?..

Answer / pradyumna171

Edit- due to unknown power factor transformers are rated in kva

Is This Answer Correct ?    0 Yes 0 No

Actually why the transformers are rated in KVA.?..

Answer / kanchan kumar

This is becoz variable loss i.e copper loss is proportional to current and fixed loss i.e iron loss is proportional to voltage hence by combinig the both losses it will be product of current and voltage hence that is why rating is in VA ie due to high value it is in KVA

Is This Answer Correct ?    1 Yes 1 No

Actually why the transformers are rated in KVA.?..

Answer / pradyumna171

Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N:B . Transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA PANDA BRG
Mob No. 9437917849

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between voltages or potential difference? And what are they?

0 Answers  


What is flow meter?

2 Answers  


Can we use LT(150 sq. mm) cable in place of HT (120 sq.mm.) cable.?

1 Answers  


What is the maximum load of 240mmsequre single core cable can carry?

1 Answers  


what is diff kav & kvarh?

3 Answers  


Are same transformer be employed for step up and step down services?

3 Answers  


what the different types of cables used for 11kv and 33kv over head work and what is the size of cable in sqmm.

2 Answers   Ordnance Factories Board,


WHAT IS THE USAGE OF Buckoltz relay IN POWER TRANSFORMER AND AND HOW ITS FUNCTIONS?

3 Answers  


How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.

0 Answers  


working principal of online ups

0 Answers   Delta Power Systems,


In what voltage EHT works(133/132/33/66kv?

3 Answers   Adhunik,


If DG runing time Neutral earth connection Dissconect what will be the effect in load and equipments.

3 Answers   GE, HP, Reliance,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)