Actually why the transformers are rated in KVA.?..

Answer / pradyumna171

Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the
real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO KNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply.

PRADYUMNA CHANDRA PANDA
Mob No- 9439721208

Is This Answer Correct ?    8 Yes 0 No

Actually why the transformers are rated in KVA.?..

Answer / pradyumna171

Edit- due to unknown power factor transformers are rated in kva

Is This Answer Correct ?    0 Yes 0 No

Actually why the transformers are rated in KVA.?..

Answer / kanchan kumar

This is becoz variable loss i.e copper loss is proportional to current and fixed loss i.e iron loss is proportional to voltage hence by combinig the both losses it will be product of current and voltage hence that is why rating is in VA ie due to high value it is in KVA

Is This Answer Correct ?    1 Yes 1 No

Actually why the transformers are rated in KVA.?..

Answer / pradyumna171

Transformer gives apparent power,it is the supply power to load and the power actually used by the load is the real power/true power/active power. Apparent power of 100 KVA has capacity to give 100 KW resistive load and for inductive load of o.8 pf it give 80 KW,and at 0.7 pf the same has capacity to give 70 KW . but the manufacturing company does not know which type of load to be connected across the transformer,therefore in simple we can say " DUE TO UNKNOWN POWER FACTOR THE TRANSFORMER ARE RATED IN KVA" and it is meaning less discuss about Iron loss & copper loss because the Inverted and UPS are rated in KVA but there is no iron loss & copper loss And in other hand in DC Generator there is Iron loss &copper loss but it is rated in KW not in KVA, because there is no angle between current and voltage(pf) in DC supply N:B . Transformer capacity -transformer iron loss & copper loss = transformer efficiency in KVA
PRADYUMNA PANDA BRG
Mob No. 9437917849

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

IN OLTC we observed "OUT OF STEP" Alarm, we have two different transformer, when both are in parallel this type of alarm observed. what's the meaning of this alarm and why it occurs???

3 Answers  


The 3 phase 400 hp 440 volt slip ring induction motor do not take one phase amps why ? The motor is running good condition

0 Answers  


What types of high speed CMOS circuits have you designed?

0 Answers   Ansal Housing, IBM, Intel,


i need some project topics along with circuit diagram in the electrical adnd electronics engg and also give ome website regarding projects.my mail id is thenmozhi2k7@gmail.com .please help me.

0 Answers  


What is the difference between MCCB and MCB ?

4 Answers   Siemens,






how ti maintain the power factor in power generation

1 Answers  


What is the RME and explain the full form and what is the RME work?

0 Answers   JLL,


what happened when we supply a dc current in dc motor?? can it worked properly?

0 Answers  


I had applied for JE in PSEB, Can you pls send me the Question bank for related to my field

0 Answers  


One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?

1 Answers  


why do select 11000v rubber mat even we use only 415Volts

1 Answers   Saint Gobain, Tata Steel Limited,


how many test is necessary for 27mva transformer.

3 Answers   HEG,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16637)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)