Can earth resistance be measured without connecting the
earth electrode?
and should earthing connections be disconnected
What is the effect of connecting two cables of different
sizes in parallel with supply?
Thanks in Advance.
I am intrested to get in touch with some
tecnocrats/engineers,my mail i.d is :
hiremathvijay@rediffmail.com
Answer / k.prakashchandra
If you want to measure ER of particular electrode ,you have
to disconnect it , to avoid the influence of other electrode
connected to the same equipment.If the cables are connected
in parallel ,the load sharing is inverse to the resistances
of cables so that the voltage drops in the cables are equal
Is This Answer Correct ? | 0 Yes | 0 No |
when giving a supply to wounded coil it will get magnetised, but the same is not if it is not wounded on a core..and it is getiing short....why.......
What safety precaution are to be taken for avoiding electric hazards ?
what are the different methods for the starting of a synchronous motor.
how to calculate lighting for a room
What is the main uses of VCB & ACB?
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
can we synchronize star system generators with delta system generators?
in a transmission line the aluminium cor is sarrounded and in between there is a another type of matrial what is that?
Why Indian Electricity frequency desined 50 Cycles as developed countrys are using high frequency with low voltage
what is wore of PLC ?
How to run 1ph motor(230 VOLTS its full load amps is 4.5 ampa))with 480 volts main(we didn hav neutral)Thn we go for step down transformer.Our load 10 amps,so we conisder this amps in primary are secondary side
WHAT IS MEANT BY BTU OF AIR CONDITIONERS.