Answer / alamgir
Formula: MF= CT Ratio * PT Ratio
Where- CT-Current transformer.
PT- Potential Transformer
Example : CT Ratio: 120/5 , PT Ratio: 11KV/110V
Ans. MF- CT* PT
=120/5*11000/110
= 24*100
= 2400
So M.F =2400
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / raj bhoyar
M.F. = (CTRatio Of CT./CT Ratio of meter)*(PT ratio of PT / PT ratio of Meter)
if values feed otherwise null values will be treated as 1 not zero.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / davinder singh
My D.G Meter Ct Ration 600/5
line volts 0.66/3.0kv
please tell me what is ans. in kw
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / dk
Suppose CT ratio 100/5 then MF will be 20
then If you want to know the consumption so you
(Total Reading *MF)= Total Consuption
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / debraj bose
Dlms meters:-Installed ct*installed pt/meter pt*mtr ct(assuming meter ct,pt
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / prabakaran
Energy meter M.F = CT ratio*PT ratio
Example:
CT ration = 120/5,PT ratio = 11KV/110
M.F = CT ratio*PT ratio
= 120/5,*11000/110
= 2400
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / manish borle
M.F.Of any energy meter is
M.F.=C.T. Ratio * p.T. Ratio * scale factor of the meter
Eg for ctr = 50/5 , ptr = 11000/110 , sf = 1/100
M.F. = 10
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / nidup dorji
If LV ring CTR = 400/1A and if the Meter CTR is 800/5A wthat will be the MF= ?? please help me
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between Floot charge and Trickle Charge.
When can we take Neutral as common neutral link?
how synchronous generator can be used as synchronous condenser?
If the Brush of DC motor is shifted by 90 deg, then what happens to voltage and torque? Both voltage and torque are zero. how to justify the answer?
What is meant by class of CT&PT?
why reactor is connected before capacitor in APFC panel
difference bteween neutral grounding resistor and neutral grounding transformer??
what is the per unit cost of generation of electricity at thermal,hydro,desael,solar,gas power plant
what is high and low cut off voltage of BB and DG at SPS????????
Disadventage of cable-gland earthing if any ?
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?
what should be the ideal gauge of wire (In sq mm) for different loads in Ampere?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)