IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO
11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE
LOADED ABOVE THE SOURCE GENERATOR RATING?
Answers were Sorted based on User's Feedback
No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / hareesh k.s.
No.
The source generator rating is 100X1000VA/415X1.73=133A
therefore the maximum load that can bear by the source of
power supply is 133A.
but the tranformer maximum output
current=500KVA/11KVX1.73=26A.
therfore the maximum load rating that can bear by the
trasformer is 26A.
ie.500KVA,11KV transformer can loaded upto only 26A.
but the maximum source KVA is 100KVA
therefore the maximum output load rating of
tranformer=100KVA/1.173X11KV=5.25A
so the conclusion is in this case the tranformer can be
loaded upto 5.25A(11KV).
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ben
firstly a 100kVA 3-phase WYE generator will only produce 100kVA of power, this will also more than likely be rated at 0.8 power factor meaning the true power you will receive will only be 80kW.
if you are using a 500kVA, 415V/11000V step-up transformer you will probably find that the 100kVA generator is not large enough to saturate the transformers magnetisation current. i would have to say you need either a larger generator or a smaller transformer to suit your site needs.
In answer to your questions: No it can not.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is XLPE type cable
I am an electrical contractor in noida, I am registereg in noida vat. i got a contract in Delhi State, my party told me that we shall deduct WCT @4% & reimburse Service tax all in composite scheme. Now Problem is this, 1 Can i able to purchase outside the delhi? 2 Can i produce a c form to our vendors? 3 What is limitation of purchase from outside the Delhi? 4 What % of tax Govt will levied upon me? 5 How can i take credit of tax paid upon purchase made by us. So, like these type questions i have in my mind if any person know the right answer please write to sksproj@gmail.com or contact me on - 8010076534 / 9212758177 / 9718378190. Thanks with Best Regards, S.K.Saxena
how starting current in motor is reduced in case of motor in star connection.
Hello, I am just preparing my self for a university interview and struck on the 11kv ring main unit system network. I just know that ring main unit has total three breakers, fuses and use to supply a power to any load/ building without any interrupt. But i am not be able to visualize the connections, either Ring main unit getting power from two different power sources? or there is always one feeder in complete ring circuit??? I would be highly thanks full of you help me.
Why transformer rating in kVA not in kW?
how to calculate KA rating of C.B?explain with Formula.
Difference between On Line capacitor and Station Type capacitor.
what is differance between kvarh $ kvah
Which are Electrical componet and Electronics componet??
Why are tertiary windings used in transformers?
what is the difference between KW and KWh?
What is duty cycle for HT motors? How many start permitted if mentioned as 01 for hot and 02 for cold per duty cycle?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)