Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO
11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE
LOADED ABOVE THE SOURCE GENERATOR RATING?

Answers were Sorted based on User's Feedback



IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / k.prakashchandra

No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator

Is This Answer Correct ?    6 Yes 0 No

IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / hareesh k.s.

No.
The source generator rating is 100X1000VA/415X1.73=133A

therefore the maximum load that can bear by the source of
power supply is 133A.

but the tranformer maximum output
current=500KVA/11KVX1.73=26A.
therfore the maximum load rating that can bear by the
trasformer is 26A.

ie.500KVA,11KV transformer can loaded upto only 26A.

but the maximum source KVA is 100KVA
therefore the maximum output load rating of
tranformer=100KVA/1.173X11KV=5.25A

so the conclusion is in this case the tranformer can be
loaded upto 5.25A(11KV).

Is This Answer Correct ?    6 Yes 1 No

IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / karthik.j

No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator

Is This Answer Correct ?    3 Yes 1 No

IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / ben

firstly a 100kVA 3-phase WYE generator will only produce 100kVA of power, this will also more than likely be rated at 0.8 power factor meaning the true power you will receive will only be 80kW.

if you are using a 500kVA, 415V/11000V step-up transformer you will probably find that the 100kVA generator is not large enough to saturate the transformers magnetisation current. i would have to say you need either a larger generator or a smaller transformer to suit your site needs.

In answer to your questions: No it can not.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the method of earthing of a transformer using electrodes?

0 Answers  


can we use CBCT in neutral of solidly grounded transformer? in place of three phases we can pass only one phase which decreases the size of CBCT?

0 Answers   UPSC,


In VSD (variable speed drive)I/P and O/P connections given wrongly what will happen?

5 Answers  


If we have 15000kw connected load in a factory than how much power demand sanction should be taken from electricity board. Pls provide complete calculation.

3 Answers  


Write down the name of 2 lady Bir Pratin of Bangladesh

0 Answers  


What is the difference between power,voltage,current? and with example

3 Answers  


What are the difference between these terms ? e.m.f, voltage, potential, potential difference, current etc? what are the difference between these terms ? (electromotive force) e.m.f, voltage, potential, potential difference, reference potential, reference potential difference, current. How can i explain and describe these all terms in single line each and little more explaination too thanks

2 Answers   Siemens,


WHY POLARITY TEST OF CT IS VERY IMPORTANT IN SWITCHGEAR

3 Answers   Birla, Reliance,


What is x/r ratio?

1 Answers  


How to test IR testing &amp; magnetic balance test

0 Answers  


The company is wiling to buy you 5 pcs of equipments in your electrical tool kit. Plz tell what are the 5 things you want?

3 Answers  


What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)