Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO
11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE
LOADED ABOVE THE SOURCE GENERATOR RATING?

Answers were Sorted based on User's Feedback



IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / k.prakashchandra

No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator

Is This Answer Correct ?    6 Yes 0 No

IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / hareesh k.s.

No.
The source generator rating is 100X1000VA/415X1.73=133A

therefore the maximum load that can bear by the source of
power supply is 133A.

but the tranformer maximum output
current=500KVA/11KVX1.73=26A.
therfore the maximum load rating that can bear by the
trasformer is 26A.

ie.500KVA,11KV transformer can loaded upto only 26A.

but the maximum source KVA is 100KVA
therefore the maximum output load rating of
tranformer=100KVA/1.173X11KV=5.25A

so the conclusion is in this case the tranformer can be
loaded upto 5.25A(11KV).

Is This Answer Correct ?    6 Yes 1 No

IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / karthik.j

No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator

Is This Answer Correct ?    3 Yes 1 No

IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE ..

Answer / ben

firstly a 100kVA 3-phase WYE generator will only produce 100kVA of power, this will also more than likely be rated at 0.8 power factor meaning the true power you will receive will only be 80kW.

if you are using a 500kVA, 415V/11000V step-up transformer you will probably find that the 100kVA generator is not large enough to saturate the transformers magnetisation current. i would have to say you need either a larger generator or a smaller transformer to suit your site needs.

In answer to your questions: No it can not.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is XLPE type cable

8 Answers   Areva,


I am an electrical contractor in noida, I am registereg in noida vat. i got a contract in Delhi State, my party told me that we shall deduct WCT @4% & reimburse Service tax all in composite scheme. Now Problem is this, 1 Can i able to purchase outside the delhi? 2 Can i produce a c form to our vendors? 3 What is limitation of purchase from outside the Delhi? 4 What % of tax Govt will levied upon me? 5 How can i take credit of tax paid upon purchase made by us. So, like these type questions i have in my mind if any person know the right answer please write to sksproj@gmail.com or contact me on - 8010076534 / 9212758177 / 9718378190. Thanks with Best Regards, S.K.Saxena

3 Answers  


how starting current in motor is reduced in case of motor in star connection.

4 Answers   Adhunik,


Hello, I am just preparing my self for a university interview and struck on the 11kv ring main unit system network. I just know that ring main unit has total three breakers, fuses and use to supply a power to any load/ building without any interrupt. But i am not be able to visualize the connections, either Ring main unit getting power from two different power sources? or there is always one feeder in complete ring circuit??? I would be highly thanks full of you help me.

1 Answers  


Why transformer rating in kVA not in kW?

5 Answers   ABB,


how to calculate KA rating of C.B?explain with Formula.

1 Answers  


Difference between On Line capacitor and Station Type capacitor.

0 Answers  


what is differance between kvarh $ kvah

1 Answers  


Which are Electrical componet and Electronics componet??

2 Answers   KarMic,


Why are tertiary windings used in transformers?

2 Answers  


what is the difference between KW and KWh?

9 Answers  


What is duty cycle for HT motors? How many start permitted if mentioned as 01 for hot and 02 for cold per duty cycle?

1 Answers   GVK,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)