IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO
11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE
LOADED ABOVE THE SOURCE GENERATOR RATING?
Answers were Sorted based on User's Feedback
No. Tranformer is for only stepping up the voltage, not the
power which should not be allowed to rise above the
capacity of the generator
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / hareesh k.s.
No.
The source generator rating is 100X1000VA/415X1.73=133A
therefore the maximum load that can bear by the source of
power supply is 133A.
but the tranformer maximum output
current=500KVA/11KVX1.73=26A.
therfore the maximum load rating that can bear by the
trasformer is 26A.
ie.500KVA,11KV transformer can loaded upto only 26A.
but the maximum source KVA is 100KVA
therefore the maximum output load rating of
tranformer=100KVA/1.173X11KV=5.25A
so the conclusion is in this case the tranformer can be
loaded upto 5.25A(11KV).
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ben
firstly a 100kVA 3-phase WYE generator will only produce 100kVA of power, this will also more than likely be rated at 0.8 power factor meaning the true power you will receive will only be 80kW.
if you are using a 500kVA, 415V/11000V step-up transformer you will probably find that the 100kVA generator is not large enough to saturate the transformers magnetisation current. i would have to say you need either a larger generator or a smaller transformer to suit your site needs.
In answer to your questions: No it can not.
| Is This Answer Correct ? | 0 Yes | 0 No |
why inverter rating is in KVA
What is the diffrence between ofline ups and online ups?
what are transmission line parameters and transmission line constants?
What is various types of electrical formula?
Why reactors use before incoming of ac vvfd drive?
why America use 60HZ 110V?
how do you test tachos and servos
1.Why hydrogen used for cooling in generators 2.Why electrical equipment protected by ground 3.Why earthing for transmission line 4.What is rms value of half wave rectified square wave. If Rms value of actual wave 2amps.
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
How capacitor improves pf
Atwhat condition reverse power relay will act?
Differentiate between digital phase converter and ordinary phase converter.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)