Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why tripping not occur when the transmission lines (11KV &
above) breaks? Doesn't
we provide earthfault protection for it?



Why tripping not occur when the transmission lines (11KV & above) breaks? Doesn't we prov..

Answer / k.prakashchandra

All the tr lines should be provided with EF protection.11
and 33 KV lines are provided with 2 OC and 1 EF relays or 3
OCR and 1 EFR.The unbalanced current passes through the EFR
which is usually set at 20% of OCR setting.The EFR is
connected between star points of CT's and relays. For
higher voltages distance relays are provided with OCR and
EFR as back up protection.If the line breaks i.e.a
conductor opens out without touching earth .The distance
relay does not act as there is no heavy current.The EFR
will trip only if the unbalanced current exceeds the set
value .Hence there will not be any tripping if the line is
not loaded sufficiently. OCR=over current relay, EFR =earth
fault relay

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What are thermo couple cables and where they are used.

2 Answers  


I would like to know that the fault curretn at base load and at 10% generation will be same? Fault level of BUS remain same with different generation?

0 Answers  


what is the benift of HT metering & LT metering

1 Answers  


what is derating?, why it is neccesary, it is same for all means for drives, motors,and cables.

1 Answers  


why ct mensioned 0.5/5p20 plese any reply to me

2 Answers  


which type motor r use in the celling fan.....

6 Answers  


What is the maximum current carrying capacity for both copper and aluminium cables for 1sqmm?

2 Answers  


What exactly is meant by harmonics and harmonic current?? and what is skewing with regard to this??

2 Answers  


How does zener phenomenon differ from avalanche breakdown?

0 Answers  


What is the difference between lubricating oil and insulating Oil?

4 Answers   Orchid,


I have two power supply.a)govt. power b)Captive power.3 phase load connected inside factory.when source change govt. source to captive some motor rotate reverse. Is phase sequence changes when if off & on?If I off generator & on it again is it possible to get changed phase sequence??

4 Answers   ABB,


On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Current: 693A Voltage:294/20KV OLTC Type: T III Y1000 110/c 12193w Max Operation Current: 295A Step Voltage: 550V Arrangement in Tx windings: Y Connection Problem: Damage of Unit 1 Generator Transformer On Load Tap Changer (OLTC) Description of Incident: 9.00 a.m. :- Generator No Load test on excitation system started 10.30 a.m :- Carried out AVR change over test 11.30 a.m :- Preparation for Generator Manual Synchronizing test 12.00 a.m :- Manual Synshronizing test started. Observed incoming generator voltage higher than running voltage. CECR operator operated Generator Transformer OLTC to bring down the incoming generator voltage 12.03 a.m :-Generator Transformer abnormal alarm operated at Gen.Control Desk (CECR) CECR operater at Generator transformer bay informed that the transformer oil splashed out from OLTC. CECR operater informed that he heard explosion inside OLTC. Observed Oil level & Oil Flow alaram operated at Tranformer local annunciator. 12.05 am :- CECR operator 'Open Gen Field Breaker” 12.10 a.m. :- Elec1 team inspected the OLTC and found the OLTC rupture disk was broken and oil spilled at OLTC area. - Elec1 found the OLTC top cover bulging. Do anyone know why and possibility cause happen in this OLTC.

9 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)