On load tap changer (OLTC) explode?
Transformer
Vector group: Ynd11
Rated Power: 353MVA
Rated Current: 693A
Voltage:294/20KV

OLTC
Type: T III Y1000 110/c 12193w
Max Operation Current: 295A
Step Voltage: 550V
Arrangement in Tx windings: Y Connection

Problem: Damage of Unit 1 Generator Transformer On Load Tap
Changer (OLTC)

Description of Incident:
9.00 a.m. :- Generator No Load test on excitation system
started

10.30 a.m :- Carried out AVR change over
test

11.30 a.m :- Preparation for Generator Manual Synchronizing
test


12.00 a.m :- Manual Synshronizing test started.
Observed incoming generator voltage higher than running voltage.
CECR operator operated Generator Transformer OLTC to bring down
the incoming generator voltage

12.03 a.m :-Generator Transformer abnormal alarm operated at
Gen.Control Desk (CECR)
CECR operater at Generator transformer bay informed that the
transformer
oil splashed out from OLTC.
CECR operater informed that he heard explosion inside OLTC.
Observed Oil level & Oil Flow alaram operated at Tranformer
local annunciator.

12.05 am :- CECR operator 'Open Gen Field Breaker”

12.10 a.m. :- Elec1 team inspected the OLTC and found the
OLTC rupture disk was broken
and oil spilled at OLTC area.
- Elec1 found the OLTC top cover bulging.

Do anyone know why and possibility cause happen in this OLTC.

Answers were Sorted based on User's Feedback



On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / mushtaq ahmed

Dear Sir, The OLTC of Generator Transformer should not be operated when Generator is in parallel with Grid. OLTC step change introduces a step voltage difference, which results in very high circulating currents. Generator AVR takes some time to adjust to this new voltage. But by that time, a very high current has flown thru the circuit. OLTCs are not rated for this, especially during changeover.

Is This Answer Correct ?    6 Yes 1 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / k.prakashchandra

Generator voltage is decided by excitation and not by OLTC which is provided on HV side . If the voltage on Generator side ( LV ) is reduced with OLTC ,then the voltage difference will be more resulting in more current due to poor lagging pf . AVR maintains the set voltage if apfc mode is not selected . This happened due to wrong operation of OLTC and loose contacts in OLTC . You could have equalized the voltage operating AVR voltage control .

Is This Answer Correct ?    1 Yes 1 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / jayesh n patel

failure is happend after tap operation , chances of contact stucking in between positions and full load current passes more time through transition resistance( as per design current passes for 60 to 90 mili seconds only, while snape action)and it got burnt ,and voltage has cut with big spark, sudden pressure has develop in side the tank and oil has got expand which result in bulging of top cover and oil spread,(mechanical failure result in electrical failure).

Is This Answer Correct ?    0 Yes 0 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / sakono

May be explode from
1. During moving the OLTC contact, some part was lossen and
OPEN circuit occure.
2. Some material of OLTC was fail and loosen. then the OPEN
circuit was occure in OLTC.
3. Contaminate inside OLTC chamber
4. Oil was contaminated
5. TAP Position of OLTC was not in step.

Is This Answer Correct ?    1 Yes 2 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / jayesh n

 while contact changing if it stuck in between position and if full load current is pass more time from transition resistance than resistance got break and heavy spark has occure, due to which sudden  pressure develope in side the oltc tank and top cover got bulged and oil spread out side the tank (transition resistance is carrying current for short time only that is  60 to 90 miliseconds only, while contact snapping action).

Is This Answer Correct ?    0 Yes 1 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / j.kesavan

oltc always problem,why its opration is motorised in auto
cotrol ,thats why disc breake every time

Is This Answer Correct ?    3 Yes 5 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / sudheer

please check the OLTC inside
connections ,carefully .because some times the connector
plate rollers not touch properly. so the winding temp.
increases continuously and oil will over-heated.

Is This Answer Correct ?    1 Yes 3 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / j.ikesavan

my friend please check your inter lock system how to
working motor on load tap changer your winding failure its
going up and down voltage thats why this disc is breake.

Is This Answer Correct ?    1 Yes 4 No

On load tap changer (OLTC) explode? Transformer Vector group: Ynd11 Rated Power: 353MVA Rated Cu..

Answer / brad stroh

where did this happen at? what is your location? we
specialize in failure analysis.

Brad Stroh

alineeds.com

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

1. which type of transformer connection is preferred in case of power supply transformers? (A) Star/Star (B) Delta/Delta (C) Star/Delta (D) Zig Zag/Star 2. In a power transformer usuall which winding is closer to the core? (A) Primary winding (B) Secondary winding (C) Low Voltage winding (D) High Voltage winding 3. The power factor of a purely inductive load is (A) Zero (B) Lagging (C) Leading (D) Unity.

9 Answers   CECRI_Central_Electrical_Research_Institute,


what is pulverisation

2 Answers  


how many testing is necessary for 27 MVA transformer?

1 Answers  


For an 100kw generator, only 50kw of load is connected. Will the generator generate only 50kw or 100kw. If it generate 100kw what happens to rest of the 50kw. What happens if we connect more than 100kw of load?

2 Answers   L&T,


on whcih cycle does gas turbine works?

2 Answers  






What is the loss of transformer of 220kv/11kv, 63/80 MVA and 18.05% impedance

0 Answers  


what is the difference between AHU and FCU .

1 Answers   JLL,


why we usually call 415 volts instead of 440 volts

3 Answers   S Tech,


When we change the tap position of 10MVA transformer it suddenly tripped with Out of step indication and also with Static differential relay indication, Transformer Bucholz relay indn and Low oil level indication. Before 1 week the same problem occured by changing the tap position. but at that time only oltc bucholz relay activated. After testing the TxR Relay team & PET team cant find any solid reason. The values are ok also. So plz answer wat's the reason for this incident? anybody plz help.

3 Answers  


what is the principle of operation of tungstun bulb ??

0 Answers  


what iz second and fifth hormonics please explain

1 Answers   Satia,


What is the Different Between Breaker and One and half breaker.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)