what is the role of impedance in transformer?based on
secondary f.l.current(139 amps) and impedance(4.07) of
415/415v of 100 kva transformer. what is the primary
current?
Answer / ma.amulraaj,b.e. mba.,
It is %impedance Voltage.In Transformer,%impedance Voltage plays significant role .Here 100KVA,11KV /415 V.
Full load current Sec .current= VA / 1.732x V (Sec.Voltage)
=(100x 1000 )/(1.732x415 ) =139 Amps, ok
Full load current Primary .current= VA / 1.732x V (Primary
Voltage)
=(100 x 1000)/(1.732 x 11000)
=5.25 Amps
Here ,the full load secondary current is 139 Amps,the rated secondary voltage is 415 V,we can do Short circuit test by applying secondary voltage 415 V,we cannot get the full load secondary current,due to impedance of Transformer.Then we have to raise the secondary voltage gradually, at particular voltage it delivered the full load secondary current,note down the voltage say 440V.From that voltage we have to find out % impedance.440 /11000 = 4% %Z=4.0 %.As this case %Z=4.07,ie. it is (4.07 x11000)/100 =447.7 V.It means This transformer may delivered a full load current at 447V.
This % Impedance may vary from Transformer to Transformer.
Is This Answer Correct ? | 3 Yes | 1 No |
On Which Pressure PRV is operated.
what is ground fault current? is there any current flow takes place through ground? is it possible? if it's possible whether it affect human beings on earth near the fault or not?
What is the function of neutral CT in transformer? Turn ratio of typical CT for 2MVA transformer ? or relation between full load current of transformer and neutral CT ?
1 Answers Electrical Inspectorate,
electricity requires a medium to flow and it cannot flow through air. so how does lightning come to earth through air without any medium?
what is the minimum pay scale for electrical engineer (building construction)in kuwait? plz revert back with yrs of experience & pay scale respectively.
what is the difference b/w conductor and semicoductor
why generator efficiency is more in swinburnes test?
A group of machines (wind turbines) connected with 33KV feeder and each machines are having individual VCB. The 33KV feeder connected with 110KV/33KV substation. The 33KV feeder tripped by over current at Substation and fault recorded at Substation as OC-R&Y phase. Same time the group of machines VCB tripped by over voltage, the fault recorded voltage was above 66KV by numerical Under/Over voltage relay. While grid drop time, this much of voltage hike is possible?
Application wise, where we should use AC motors and where we should DC motors?
where does core based current transformer is used? and what is the value of lux in a work station?
1.What is the range of stator resistance of 3-phase induction motor? 2.Two electrically operated vibro motors are foxed in parallel direction in vibrating feeders. what is the direction of both vibro motors?
what is the ms flat constant for calculating earth mat design calculation?