What type of protective system we uses in L.V. distribution
panels?
Answers were Sorted based on User's Feedback
Answer / satya dev
1-Over current & earth fault relay for feedar Protection.
2-reverse power relay for Alternators ( if diffrent
sourcees are used- eg. transformer supply & DG supply)
3-Inverse/differetial relay for Busbar protection.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / vel
over current and earth fault relays (2OL+1EL method)are
used for lv .
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / jagadisha.n bmsit
Different protection systems which is used in LV panels are:
1. Short circuit protection :- It is done by choosing set
point in sc protection relay which is present inside the CB's.
2. Thermal protection for Busbars/ cables:- Bec extreme
thermal point cause flash over
3. Over current protection
4.Protection provided by proper shielding & interlocks such
that operator & maintenance people can not accesses live parts
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sachin
1.over current reley
2.earth fault reley
3.fase failure relay
3.fuse moniterning relay.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / nagesh
current protection
1)over current
2)short ckt current
3)Instantanious current
Earth fault relay,
Negative phase sequence
Phase failure
If require
High temprature
High vibration
Safety (door switches)
MD over shoot(MD monitoring)
Is This Answer Correct ? | 0 Yes | 0 No |
what is earthing
how make to Incident and accident report
how can decide the current rating of oltc
Practical condition in 400KV Sub station:- Breaker(open) , isolator(open), Earthing (close) at both end e.g A & B. Now Open A Stn Earthing than Open B stn Earthing (Which have a 50MVA reactor) , AND suddenly show R,Y,B phase 704KV,573KV,118KV respectively. Que is without closing of breaker how it is possible.???? My Whats app No:07621840498 for Further Discussion. Pls experts suggest.
for 750 kw LT load what will be the ht kva
when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??
how to improve power factor correction?
I want to know how to calculate the size of electricity cable in building?
0 Answers DR Engineering Services,
What is the effect of positive feedback on stability of the system?
what is the difference betn earthed and unearthed cables which is commanly used why?
what is parellel power factor correction?
Why we use 4-20 mA Analog signal for the PLC input? Why not 0-20 mA? Why not 5-25 mA?