Answer / vasanth
to regulate the excitation voltage in generator AVR is used.
it compares the voltage, current and frequency of the
generator.
| Is This Answer Correct ? | 150 Yes | 25 No |
Answer / sivakumar
AVR is an abbreviation for Automatic Voltage Regulator.It
is important part in Synchronous Generators, it controls
the output voltage of the generator by controlling its
excitation current. Thus it can control the output Reactive
Power of the Generator
| Is This Answer Correct ? | 66 Yes | 7 No |
the fullform of avr is Autometic voltage regulator,
basically avr is used in transformer and genrators.
in transformer it works with PT and a tap changer motor
which autometically change the tap to control the voltage.
in genrators avr sense the voltage with the help of PTs and
control the exciting current in exciter to canrol the
voltage.
| Is This Answer Correct ? | 32 Yes | 9 No |
Answer / satish babu
AS the name itself indicates it is a device which maintains
the required output terminal voltage & hence called as
Automatic voltage regulator,
a) In case of alternators the Terminal Voltage(TV) is ref.
& whenever the TV tend to fall due to load the drop is
immediately sensed & excitation is increased thereby the
required voltage is maintained in the output terminals.
b) In case of transformer the PT output is the ref. As the
voltage drops due to load an immediate signal is given to
Tap changer motor (raise/lower)which varies the tap
position in the transformer thereby achieving the required
Terminal voltage.
In Both these equipments AVRs are used,which is an
electronic device which has an inbuilt comparator &
regulator.
| Is This Answer Correct ? | 16 Yes | 5 No |
Answer / v.k.rajput
AVR increase or decrease excitation voltage for linear
voltage.Frequency depends on primover speed.
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / senthil kumar
It is important part in Synchronous Generators, it controls
the output voltage of the generator by controlling its
excitation current and thus , it could control the output
Reactive power of the generator.
| Is This Answer Correct ? | 17 Yes | 10 No |
Answer / er. jackson s.
AVR stands for Automatic Voltage Regulator.
It is a device used to maintain a constant voltage at the
alternators terminals. It functions by maintaining the
excitation required to maintain the terminal voltage of the
alternator with change in the load.
Increase in excitation voltage increases reactive voltampere
(var) which decreases powerfactor (cos(phi)).
generally, voltage(V) of the alternator is kept constant so
thE rest of the components in VIcos(phi), ie. I and cos(phi)
have to vary according to the load.
Increase in I causes decrease in Pf and Decrease in I causes
increase in Pf.
so it is clear that Excitation V is proportional to var and
load current (I) and inversely proportional to power
factor(cos(phi)).
hope this helps.
| Is This Answer Correct ? | 12 Yes | 6 No |
Answer / elec.eng.babikir sharief
The AVR is control output voltage come from genrator by
measueing the voltage output, used to make stablity and
protaction genset
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / jai prakash narain singh
AUTOMATIC VOLTAGE REGULATOR(AVR) IS PART OF THE EXCITATION
SYSTEM OF A ALTERNATOR,WHERE IT REGULATE THE GENERATOR
OUTPUT VOLTAGE BY INCREASING/DECREASING THE EXCITATION
CURRENT OF EXCITATION FIELD.
THE PURPOSE OF AVR IS TO BUILD UP RESIDUAL VOLTAGE TO
NOMINAL VOLTAGE LEVEL AND MAINTAIN THE NOMINAL VOLTAGE
IRESPECTIVE OF LOAD,in addition to regulating generator
voltage,the avr circuitry includes under speed and sensing
loss protection features.excitation power is directly
derived from the generator terminals.
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / vinoth.m
AVR - Automatic Voltage Rwgulator which is normally used in
ups to supply a regulated output to the load.
| Is This Answer Correct ? | 5 Yes | 3 No |
CT Ratio of a energy meter connection is Red Phase : 100/5A, yello Phase : 50/5A & Blue phase : 100/5 A what is the overall Multiplication factor
234 MVA Generator 3 phase Short circuit current Values required? Gen set Rating-234 MVA, Gen Voltage-18kv, PF;0.8, Xdv:23.5 %, Transformer Rating-18/380KV, 680MVA,Yndd1 two winding, Step up TR, ZT:35.50 %,X/R 4.33 Gen CB Position, CB open ,Disconnected open, Generator Running Voltage 18 Kv, Bi mistakes generator side earth switch Closed during that time short circuit current level in 3 Phase required, and how to test on site 234MVA Generator Short circuit current,
What is a circuit breaker contact multiplier relay?
What are all the problems occured while ac generator running in leading power factor at full load condition?
How many types of protection relays are there based on the characteristic?
what is difference between neutral and ground wire?
How to justify this statement ??? "Capacitors in series provide less capacitance but higher voltage breakdown rating for the combination"
In how we connect watt meter for open & short circuit test of a single phase transformer.
what is phase to phase to phase to ground fault
how solar power plant energy meter multiplication factor
Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
In all electric motors, fans are provided to dissipate heat. How it dissipate the heat? By absorbing atmospheric air or by exhausting the heated air generated while running?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)