Electricty is generated at around 16kV, then step up to
220kV for transmission then steped down to power
transformers then DTs and then through the LT n/w it reaches
the consumer end.
At the consumer end 230V supply is required. So, why is
electricity not generated directly at 230V and transmitted?
Answers were Sorted based on User's Feedback
Answer / abhinav
what happened in a transmission line is that there occurs
losses while transmitting power on the transmission lines
due to the conductors.
as The higher the current then the greater the power losses
power loss = I^2R (ohmic loss)
so we prefer to step up the voltage becoz the higher the
voltage , lower is the current.
so it is always necessary to transmit the power after
stepping it up so as to reduce losses..
Is This Answer Correct ? | 16 Yes | 1 No |
Answer / hitesh
Abhinav is write as if we transmit 220volt through long
distance we need heavy conductors as current increases.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / naveen
WE KNOW ,P=VI AND P=V^2/R SO AS WE INCREASE VOLTAGE THEN LOSSES ARE VERY LESS FOR EXAMPLE IF WE TRANSMITED 10 VOLT THEN RECEIVED 100/R AND IF WE TRANSMITTED 100 VOLT THEN WE RECEIVED 10000/R.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / anil kumar verma
power is generated at power plants which are generally
situated at far distance from the actual users at 220
volts. so power has to be transmitted to these users. if
power is transmitted at 220 volts then due to high currents
at low voltage transmission losse will be very high & very
low voltage will be experienced at consumer end. so to
minimise the losses power is generated & transmitted at
high voltage. moreover generation & transmission at 220
volts will not be cost effective.
Is This Answer Correct ? | 4 Yes | 4 No |
What is the maximum load of 240mmsequre single core cable can carry?
when we connect the capacitor banks in series with the circuit?
what is tertiary winding in transformer?What is its purpose?
What is the formula to calculate capacitor bank rating for a certain load.
1. what is usage for power factor in industries?? 2.why we need to monitor power factor??
what are the different types of bus bar used at electrical work at shelter
3 Answers Aster Teleservices, Costco,
how to calculate the size of cable for 100 kva load,?can somebody tell me with a formula
What is the problem, if a circuit breaker is not closing.
why elcb used in circuit
what is interference
How to calculate cable size for a particular load? i have 12 MW,11KV Motor 3 Phase, what should be cablesize? What are the points to remember for cable sizing calculations?
How does and Earth Fault Relay operates in DG set control panel?
1 Answers Cummins, University,