Why is making current of CB always greater than CB breaking burrent?.
Answers were Sorted based on User's Feedback
Answer / john henry
Making capacity is the MAX current that a CB can pass at
the occurence of fault.
And breaking capacity is the RMS value of current at which
CB can break its contacts open.
Now when fault occurs, system goes into the subtransient
state and a huge amount of current flows in the system.
and this time if the breaker is reclosing and the making
capacity is low it will burn so it is high.
Breaking is low so that it can be isolted from the system
as soon as the fault occurs with less arching and to save
the contacts of the breaker.
| Is This Answer Correct ? | 35 Yes | 3 No |
Answer / gunasekaran
breaking current is always rms value making current are peak
current. because at the fault condition breaker will be re
closing at sub transient condition. at subtransient
condition current is more so the designed making current
value is less it will burn. so making current always more
than breaking current. it is about 2.5 times of breaking
current.
| Is This Answer Correct ? | 16 Yes | 3 No |
Answer / aqeel
Making current implies dc component so it is 2.5 times
breaking current
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / palani
The CB breaking current is less than Making current. The
breaking occur at the zero of the alternating Current where
as making occur at any amplitude of current in the
alternating current .
| Is This Answer Correct ? | 20 Yes | 18 No |
Answer / sudar
Which one more save opening CB at capasitive or inductive
condition???
| Is This Answer Correct ? | 2 Yes | 8 No |
Answer / sagar hingmire
Bcoz If making current capacity is not greater than
breaking current then if fault is there on electrical
system & ur going to close CB then very high fault current
will flow through CB and CB will get damaged or blast as
fault is not cleared.
| Is This Answer Correct ? | 6 Yes | 18 No |
what is reactive poower
Why can't we parallel the secondary circuits of two voltage transformers?
What is rms value wher it is used??????????
what happend when 230v dc motor we supplied a 23v ac supply
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
Why 11KV PT Secondaries [(11000/1.732)/(110/1.732)/ (110 / 3)]are in star connection ? And why the same should not be in delta ?
What type of fittings and electrical accessories can be install in radiation area ?
what is the difference between transformer,converter and transducer
How to find earthfault location in long cable layed underground or outside.
Why size of HT cable is less then LT cable inspite of the fact that voltage is higher in HT cable?
when we increased the current what do ?
In batteries after completion of charging which colour gas is emitted from it?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)