Why is making current of CB always greater than CB breaking burrent?.
Answers were Sorted based on User's Feedback
Answer / john henry
Making capacity is the MAX current that a CB can pass at
the occurence of fault.
And breaking capacity is the RMS value of current at which
CB can break its contacts open.
Now when fault occurs, system goes into the subtransient
state and a huge amount of current flows in the system.
and this time if the breaker is reclosing and the making
capacity is low it will burn so it is high.
Breaking is low so that it can be isolted from the system
as soon as the fault occurs with less arching and to save
the contacts of the breaker.
Is This Answer Correct ? | 35 Yes | 3 No |
Answer / gunasekaran
breaking current is always rms value making current are peak
current. because at the fault condition breaker will be re
closing at sub transient condition. at subtransient
condition current is more so the designed making current
value is less it will burn. so making current always more
than breaking current. it is about 2.5 times of breaking
current.
Is This Answer Correct ? | 16 Yes | 3 No |
Answer / aqeel
Making current implies dc component so it is 2.5 times
breaking current
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / palani
The CB breaking current is less than Making current. The
breaking occur at the zero of the alternating Current where
as making occur at any amplitude of current in the
alternating current .
Is This Answer Correct ? | 20 Yes | 18 No |
Answer / sudar
Which one more save opening CB at capasitive or inductive
condition???
Is This Answer Correct ? | 2 Yes | 8 No |
Answer / sagar hingmire
Bcoz If making current capacity is not greater than
breaking current then if fault is there on electrical
system & ur going to close CB then very high fault current
will flow through CB and CB will get damaged or blast as
fault is not cleared.
Is This Answer Correct ? | 6 Yes | 18 No |
is that any software calculator to calculate the size of cable
The power dissipated by a resistor of 10ohm when a current of 2A passes through it is:(a) 0.4W(b) 20W(c) 40W(d) 200W
what safety use in electrical panel
What are interpoles and commutation windings?Why r they used?
What is difference between mcb and mccb.
what is mean by busbar and what is the difference between busbar,transmissionline,feeder,distribution line
Should transformer earthing pit, to be connect to earthing mat in Substation
WHAT IS THE FULL FORM OF CABLE TYPE-AYWY,AYWAY,YWY ?
If there is unit power factor in a power house and a capacitor bank used in a factory at resistive load . In this case, will there leading power factor in power house across that factory.
Why efficiency of generator is higher than motor at a particular load?
Can anyone please give me the parameters , formula needed to calculate the circuit breakers for building services.Thanks
what is the isolation transformer. what is the isolator?