Answer / vinoth kannaa
capacitor banks are highly used in substations for
increasing the power factor. depends upon the load type
highly used by the consumer its value is to be selected.But
most of the loads are inductive in nature.So the power
factor will be lagging in nature.In order to increase the
power factor upto unity level the capacitor banks are
used.But during midnight time the power consumed by the
consumer are very low.At the time we require low capacitor
bank values.It can be explained by the following
equations.we know that
C=Q/V and P=(3)1/2 VIcosO
As phase angle between the voltage and current increases in
the leading side means the power factor will be increased.
| Is This Answer Correct ? | 13 Yes | 2 No |
Answer / pardeep singh
capaster bank is used in substation for example 132kv to
improve the power factor the capester bank rating is depend
upon the consumer because tn our country mostly enductive
load is used so at the day the sub station mens used
capester bank mostly but at night the consumer consumption
is less so the power factor improve ment is less at night
p=q/v
p=vicosphy
| Is This Answer Correct ? | 4 Yes | 1 No |
How the output,losses and temperature of machines varies with linear dimension?
why neutral of 6.6 kv star connected sq. cage induction motor does not get earthed, though for earth fault protection it is must.
why rating of generator is kva but motor is kw ?
how we can select a transformer based on a particular load. suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p & 100 h.p. then what rating of transformer we can select. urgent. pls reply
i have 3, 75hp motors and 10, 15 hp motors....and to run this motors continously with a generator how much rating(kva) of generator will suiteble....?
where was current transformer protection units used and why??
what is the specific gravity of fully charged battery
what is the differnce between vector and phasor? are both same or there is difference between two term.?
SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS
when the time of backcharging the transformer three phases only enough or three phase with neutral is must.from these which one is the best one.
if we give connection of 100watts bulb through a single phase energy meter ,the disc of a meter rotates why it happens?
What are the application of filter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)