what is Diversity factor in electrical installations
Answers were Sorted based on User's Feedback
Answer / noel
Diversity factor is the ratio of the sum of the individual
maximum demands of the various subdivisions of a system,
or part of a system, to the maximum demand of the
whole system, or part of the system, under consideration.
Diversity factor is usually more than one.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / k.prakashchandra
Installation, not the station ? It can be taken as' Sum of
the peak loads of individual feeders or sections '/ 'The
peak load of the installation' and it is always greater than 1
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / agbo.c.ezeh
diversity factor simply means the total connected load divided by the actual maximum load of any installation.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the dedicated neutral earth in ups? y its required?
what is the differnce between vector and phasor? are both same or there is difference between two term.?
1 unit or 1 kwh means how much kva
what is the diff between VCB & ABCB breaker in substaions? explain the operating priciples of VCB & ABCB
How to arrange a hous hold earthing system to keep minimum earth resistance( below 7ohms).
How many types oil using in transformer ? How many letars using in transformer..?
what is gridrotor resistance starter
how many units consumed by 8.5 ton ductable split ac in one hour in 3 phase?
In which connection the distribution T/F is connected? a) ▲ / Y b) Y / ▲ c) ▲ / ▲ d) Y / Y
What is the fuction of surge arrester and surge suppressor? Modern days line designes are based on which surge?
hey guys i recently saw a long transmission line in which a sort of balloons in red and white color were hanging at each section.do u have any idea why are they kept for?
Why auxiliary transformers are not connected in parallel in primary stations?