Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


We have laid the single core Armoured cable 7 nos ( 2 each
phase & 1 neutral ) to cater our electrical load .
the issue is though we have Glanded the cable both the end
also givan the earthing to the panel both the end we are
facing a heavy sparking at the gland side. what could be
the reason.

Answers were Sorted based on User's Feedback



We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / virendra

Mr sharma Please note that we have a stady system & all the
equipment is properl earthed . there is no such load like
welding machine is existing.Is it cerculating cureent ??????
as this is a single core cable

Is This Answer Correct ?    1 Yes 0 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / shantanu mishra

This is definitely a case of improper earthing. The
substation earthing is poor. The panel and armoring of cable
need to be more strongly earthed. During normal conditions
there would not be any sparking butwhen there is any fault
on 11kv line nearby, the ground potential suddenly rises and
so the panel comes at a high potential and sparking take
place between panels and armoring of cables which are not
getting proper earth.

Is This Answer Correct ?    2 Yes 1 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / shantanau mishra

Dear Virendra
have you found any solution to your problem. Pl share.

Is This Answer Correct ?    1 Yes 0 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / ahmed

Well,you need to check if you really need to glad the
cables from both side .Or check the type of glad is it
metal or non-metalic .

Is This Answer Correct ?    1 Yes 0 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / rajesh

Use special gland (Gland with bush) at the panel(load side), but ensure the proper gland earthing in first side. The above situation is due to circulating current

Is This Answer Correct ?    0 Yes 0 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / abhishek mishra

Dear Virendra
if you are using CRCA gland plate for glanding then such problem may occur. If you are using single core cables then either use aluminium gland plate or make a thin cut hole to hole in CRCA gland plate

Is This Answer Correct ?    0 Yes 0 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / ravi teja

Mr.Virendra i would like to know the details of load means
which kind of load and ur suitability of ur cable with ur load

Is This Answer Correct ?    0 Yes 1 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / virendra

Dear Ravi,

we are having a load around 300 KW with 200 KW lighting
load & 100 KW of Motive load.

Also note that we have a stable system with balance load

Is This Answer Correct ?    0 Yes 1 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / robertm

It sounds like you have a loop, check and see if the
neutral and the earthing cable are laid down on the same
bars. If this not the incoming service then that could
cause your problem.

Is This Answer Correct ?    0 Yes 1 No

We have laid the single core Armoured cable 7 nos ( 2 each phase & 1 neutral ) to cater our e..

Answer / virendra joshi

Guys,

let me clear that the earthing is proper we get the value
0.1ohm. We have used double compress gland which is fixed
in proper way, there no such thing like looping, but still
the problem is there . please share what else can be the
cause ?

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the transformer

6 Answers  


mostly the questions were from machines... d.c. machines, transformer, synchronous and induction all theory paper........ few from power system... but the level of paper was easy.....

0 Answers   IFFCO,


when neutral will carry the current?what could be the magnitude?

7 Answers   Voltas,


What are the different types of transformers present in the Transmission and Distribution system?

2 Answers  


how we can calculate the efficiency of a diesel generator ?

0 Answers  


what is meant by ceiling voltage, ceiling current?? pl reply asap

4 Answers  


what is a 3 phase power formula ?

5 Answers  


wow to calculate the transformer rating(KVA)

0 Answers  


WHY WE ARE EXPRESSING KW-HR AS UNIT OF ELECTRICITY.........?WE CAN EXPRESS IN ANOTHER UNIT.....?

4 Answers   Summit Power,


How to Select transformer for 100HP motor plz... With calculation

2 Answers   Rasandik,


what will happen if ac motor given dc supply?

1 Answers  


Hi friends, i m electrical engineer i want a cdr for migration purpose so anybody have information about this then send me on jayesh_ee88@yahoo.com.please try to me

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)