We have laid the single core Armoured cable 7 nos ( 2 each
phase & 1 neutral ) to cater our electrical load .
the issue is though we have Glanded the cable both the end
also givan the earthing to the panel both the end we are
facing a heavy sparking at the gland side. what could be
the reason.
Answers were Sorted based on User's Feedback
Answer / shantanu mishra
This is definitely a case of improper earthing. The
substation earthing is poor. The panel and armoring of cable
need to be more strongly earthed. During normal conditions
there would not be any sparking butwhen there is any fault
on 11kv line nearby, the ground potential suddenly rises and
so the panel comes at a high potential and sparking take
place between panels and armoring of cables which are not
getting proper earth.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / shantanau mishra
Dear Virendra
have you found any solution to your problem. Pl share.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ahmed
Well,you need to check if you really need to glad the
cables from both side .Or check the type of glad is it
metal or non-metalic .
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rajesh
Use special gland (Gland with bush) at the panel(load side), but ensure the proper gland earthing in first side. The above situation is due to circulating current
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek mishra
Dear Virendra
if you are using CRCA gland plate for glanding then such problem may occur. If you are using single core cables then either use aluminium gland plate or make a thin cut hole to hole in CRCA gland plate
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / robertm
It sounds like you have a loop, check and see if the
neutral and the earthing cable are laid down on the same
bars. If this not the incoming service then that could
cause your problem.
Is This Answer Correct ? | 0 Yes | 1 No |
Guys,
let me clear that the earthing is proper we get the value
0.1ohm. We have used double compress gland which is fixed
in proper way, there no such thing like looping, but still
the problem is there . please share what else can be the
cause ?
Is This Answer Correct ? | 0 Yes | 1 No |
Dear Brother can u tell the proper size selection of cable & the fault level calculation of braker, busbar etc. pls mail me at azeemk30@gmail.com
What mean by MLTP
What is process of anneling transformer core
Why is transformer connect parallel? why not series? ....plz...
Why dc shunt motor in lathe, compound motor in rolling mills
What is applied voltage for meggering a 6600V HT cable
What are the basic properties of signal flow graph?
What is difference between A.C & D.C Resistance ?
what is the difference between earthing and grounding of electric circuits
what is demagnetising effect & crossmagnetising effect and how it is related to electrical system?is there any more effects are available or only these two??
How can we define 'Phase'
Graphs of measuring power and speed on dc motor