what is the effect of PF on alternator sizing?
Answers were Sorted based on User's Feedback
Answer / gunasekaran
if PF is less KVA rating of the GENERATOR will be more
how it is KW=KVA/PF if PF reduced KVA rating is goes up for
same KW rating so genarator size will be more than
nomal.for low PF current also high so losses are high at
all stages.
Is This Answer Correct ? | 20 Yes | 2 No |
Answer / kalidassallinterview
Generaly the generator is run in lagging power factor only.
If we tryed to increase the power factor to unity, then the
generator will be overloaded.Ex: 750KVA,0.8PF generator we
can connect up to 600KW load. If we increase the power
factor to unity there is a chace to connect extra true
power up to 750KW. so the engine will be load.
Is This Answer Correct ? | 3 Yes | 1 No |
What current can be carried by 25 sqmm copper cable safely?
How to find the length of a Xlpe cable required to transmit 3mva load at 22kv.
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
Differentiate between kirchhoff’s first law and kirchhoff’s second law?
why is a earth pit 10 ft usually? And, what should be the distance betweeen two earth pit?
How can we find out earth leakage,(shock)in side the house?.. (with out ELCB)
For maintenance Department What type documention requir for ISo & TS audit
1 Answers Megatron Solutions, Sams,
Why transformer neutral is earthed
Difference between online and offline UPS?
tell me any book for current n potential trasformer with full knowledge ?
What is core CT & it's function?
Can any one tell me the current VAT, Sales Tax, Octroi and Excise duty for the financial year 2009 -2010. Say control panels are manufactured in maharashtra, then what will be the taxes for within Maharashtra and outside Maharashtra?