Answer / sam daniel, marthandam, kanyak
To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*Also, since this is linear region
*Not possible to cause spark
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
Is This Answer Correct ? | 62 Yes | 3 No |
Answer / jayaraj
1}///in earlier days we had used BJT transister in signal
conditioning circuits for amplification purposes so in BJT
transfer characteristics 4 to 20 milli amps is a linear
region,....but now-a-days we re using cmos only.... as a
convention only we are following this 4-20 range
2}///another reason...for not using 0 milli amp
coz if we use like that we cannot distinguish between true
signal zero and dead zero(break in wires)
Is This Answer Correct ? | 46 Yes | 2 No |
Answer / nileshkumar
1) 4 - 2 ma signal can transmited long distance without
signal drop in cable.
2) To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*when two connection short no sparking.
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
Is This Answer Correct ? | 5 Yes | 1 No |
in 4-20ma we can easily check the zero and wire breaking in
transmitter. Analog card accept 1-5v dc supply. thatsy V-IR
I=V/R
V=1V R=250OHMS
1/250 = 4MA
V=2V THEN I=2/250 = 8MA
V=3V THEN I=3/250 =12MA
V=4V THEN I= 4/250 =16MA
V=5V THEN I=5/250 = 20MA.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anish kumaran r
Live zero and minimum current required to keep alive the tx
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh nagdeo
another reason from starting current from 4 ma is between two cables maximum induced current is always below 4 ma. if electrical and instrumentation cables running together this type problems arised.
Is This Answer Correct ? | 0 Yes | 0 No |
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
what is o2 analyzer and how it measured ,what is the role of this analyzer in cfbc boiler...
what is the difference b/w magnetic flow meter&mass flow meter? which one is best?
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
what is difference between DO and DI
Why we use mmwc unit for pressure
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?
What is difference between Ionization heat and bimetallic heat
what is the meaning of wet leg & where is it used?
I heard that we can use flow transmitter for level measurment also hw it is?
How oil line flow measured?eplain about instruments used and working principle?
why generation of syncronized generator increases when frequency of grid is less then 50Hz & generation decreases when grid frequency goes up from 50 Hz, as comparision with set value entered in govering panel?