Why we use 4 - 20 ma?
Answers were Sorted based on User's Feedback
Answer / sam daniel, marthandam, kanyak
To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*Also, since this is linear region
*Not possible to cause spark
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
| Is This Answer Correct ? | 62 Yes | 3 No |
Answer / jayaraj
1}///in earlier days we had used BJT transister in signal
conditioning circuits for amplification purposes so in BJT
transfer characteristics 4 to 20 milli amps is a linear
region,....but now-a-days we re using cmos only.... as a
convention only we are following this 4-20 range
2}///another reason...for not using 0 milli amp
coz if we use like that we cannot distinguish between true
signal zero and dead zero(break in wires)
| Is This Answer Correct ? | 46 Yes | 2 No |
Answer / nileshkumar
1) 4 - 2 ma signal can transmited long distance without
signal drop in cable.
2) To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*when two connection short no sparking.
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
| Is This Answer Correct ? | 5 Yes | 1 No |
in 4-20ma we can easily check the zero and wire breaking in
transmitter. Analog card accept 1-5v dc supply. thatsy V-IR
I=V/R
V=1V R=250OHMS
1/250 = 4MA
V=2V THEN I=2/250 = 8MA
V=3V THEN I=3/250 =12MA
V=4V THEN I= 4/250 =16MA
V=5V THEN I=5/250 = 20MA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anish kumaran r
Live zero and minimum current required to keep alive the tx
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh nagdeo
another reason from starting current from 4 ma is between two cables maximum induced current is always below 4 ma. if electrical and instrumentation cables running together this type problems arised.
| Is This Answer Correct ? | 0 Yes | 0 No |
Make Heater Process Logic.
what are the inputs (drawings) we need to prepare loop schematics??
What is deffrence between Battery and capacitor
Hello-I know this not an engineering question,I am working in gulf & i want to do correspondence diploma in instrumentation,can any one give me the address of any university in which this courses are available.
How can we calibrate pressure and flow transmitter in the field(online)?
can u please give the exact ckt explaination of AC Drive related to industries.
Air pressure in a pressure vessel can rise or fall at up to 2.5kpa/s.The pressure is sampled every 0.5 seconds.If range of the the pressure indication is 0 to 1500 kPa, what is the max value of the error due to sampling in % of Span
what is pressure control
1 Answers GNFC, IBM, Privi Organics,
what is loop1 and loop2 in MTS LT?
Can you explain drawbacks between P,I,D & PID controller
1 Answers JSW, Priya Cement, TPL,
how we calculate the range of flow from a dp?i mean if we have a dp,3810mm h2o.how much flow ranges we can use for this DP?
can we connect instrument earth pit to electrical earth pit, if not why?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)