Answer / sam daniel, marthandam, kanyak
To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*Also, since this is linear region
*Not possible to cause spark
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
| Is This Answer Correct ? | 62 Yes | 3 No |
Answer / jayaraj
1}///in earlier days we had used BJT transister in signal
conditioning circuits for amplification purposes so in BJT
transfer characteristics 4 to 20 milli amps is a linear
region,....but now-a-days we re using cmos only.... as a
convention only we are following this 4-20 range
2}///another reason...for not using 0 milli amp
coz if we use like that we cannot distinguish between true
signal zero and dead zero(break in wires)
| Is This Answer Correct ? | 46 Yes | 2 No |
Answer / nileshkumar
1) 4 - 2 ma signal can transmited long distance without
signal drop in cable.
2) To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*when two connection short no sparking.
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
| Is This Answer Correct ? | 5 Yes | 1 No |
in 4-20ma we can easily check the zero and wire breaking in
transmitter. Analog card accept 1-5v dc supply. thatsy V-IR
I=V/R
V=1V R=250OHMS
1/250 = 4MA
V=2V THEN I=2/250 = 8MA
V=3V THEN I=3/250 =12MA
V=4V THEN I= 4/250 =16MA
V=5V THEN I=5/250 = 20MA.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anish kumaran r
Live zero and minimum current required to keep alive the tx
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh nagdeo
another reason from starting current from 4 ma is between two cables maximum induced current is always below 4 ma. if electrical and instrumentation cables running together this type problems arised.
| Is This Answer Correct ? | 0 Yes | 0 No |
How flow can be measured with dp?
my data card only does run in my mobile so how can change it that it run other mobile & computer and i can stor data in my data card
Why Ma signal is using for control system?
what is the difference between Ethernet unmanaged and managed Switch?
what are the different types of communication cables used in automation and what are the difference in the cables
Please why do we use 4-20ma in instrumentation engineering
define optical temperature detector
You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?
how can be connected thermocouple in series?what is the need?
how to calculate interface capelary level transmetar lower S.G.0.54 and uper S.G. 0.26 and h=490 mm
Control valve question what is the meaning of cauge.?what is the use of cauge?
role of electrical engineer in the instrumentation industry
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)