Air pressure in a pressure vessel can rise or fall at up to 2.5kpa/s.The pressure is
sampled every 0.5 seconds.If range of the the pressure indication is 0 to 1500
kPa, what is the max value of the error due to sampling in % of Span
Answers were Sorted based on User's Feedback
Answer / rizwan afzal
Dear
change in pressure can be +2.5kpa/s or -2.5kpa/s. while
sample rate is 0.5 sample per sec and range is 0 to 1500Kpa
so error is
e=0.5s*2.5kpa/s
e=1.25kpa
now to calculate percentage of error
%e=(100*1.25Kpa)/1500kpa
%e= 0.0833%
keep in mind error can be +0.0833% and -0.0833%
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / markwilcon
Any one able to help??
I have error = 0.5s x 2,5kpa/s=1.25 %
Is This Answer Correct ? | 0 Yes | 1 No |
What is feed factor and its Importance in cement industry? How we can solve feed factor?.
What is the main difference between Cavitation and Flashing?
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
I installed the smartplant instrument v8, but can not be opened, that always said: "INTools 2007 hardlock no found". So Could you help me how to do for that?
i want to know the interview format fot gail, instrumentation. pls answer me in habib.sami1003@gmail.com
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
all types of liquid analyzer principle with drawing?
What is ptw and write 3 types of ptw?
How can I zero check of wet leg type DP Tx ?
what is mean by TDC-3000
what is mean by hot loop and cold loop testing, whts different between both
difference between dcs & pld