How can we calibrate pressure and flow transmitter in the
field(online)?
Answers were Sorted based on User's Feedback
This procedure can be used to calibrate any type of
instrument in the field on a live plant regardless of it's
type or application. The only variation in the procedure is
what test equipment you will use to calibrate the instrument
with. For instance calibrating a temperature transmitter you
want to take a HART and decade box with you. Calibrating a
pressure , flow or DP transmitter, you want to take a HART
and pressure pump with you like a Druck or hand pump with a
precision gauge on.
The procedure:
Since the transmitter is on line and on a running plant, you
need to determine a couple of things first before you start
working on it. First and most important of all, what does it
do? Is it a control transmitter, a trip transmitter or just
a indication.
Control transmitter means it's output will go to the DCS and
is linked to a PID controller which will give a continues
output, based on this input, to a control element in the
plant plant like a control valve or a heater element. These
are all critical control components that will trip the plant
if you upset their stability.
Trip transmitter means that it is linked to the ESD system
and will start a plant shut down if it is seeing a to high
or low pressure, flow, DP or level depending on the
application you are working on. Just indication means that
it is completely safe to work on and you cannot trip anything.
To make the control transmitter safe to work on you need to
put the DCS PID controller in manual. This will keep the
output of the controller at the current output position and
bypass the output function of the controller. In a fast
moving application the control room operator will send a
field operator with you to control the control valve
manually with it's hand wheel while you work on the control
transmitter.
To make the trip transmitter safe to work on you need to put
a inhibit in the ESD system output trip function of the
transmitter. This is also sometimes refer to as a MOS
(maintenance override switch).
In both cases the control room operators will do this for
you providing that you have all the permit to work and
inhibit permission paperwork in place.
Good luck
Is This Answer Correct ? | 34 Yes | 10 No |
Answer / anjal
first close the isolation and open the equaliser if its
show zero ok other wise calibrate the transmitter
Is This Answer Correct ? | 18 Yes | 12 No |
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
can you give some devices that measure directly the mass flow rate.
how to know the URL and LRL for steam drum level and why the calibration range is in negative ?
how to relay switch sense the fault?
What is the minimum rating availalbe for weld neck orifice in market?
the 3 most common transmitter protocol being in refinery or qatar gas and aramco.
What is two wire system and how it work
IS THEIR ANY AGEING EFFECT ON FLOW NOZZLE, ORIFICE, MANIFOLD, OR TRANSMITTER ?
1.In which princeple DP transmeter works? 2.Why UPS system is use for DCS? 3.How drum lvel controller works? 4.What is the difference between glob valve and gate valve? 5.How axial shift probe work & in which princeple it works?
1 Answers Luberef, Qatar Gas, Reliance,
please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?
which one is best profibus or RS485 for communication?
It is desired to reduce effect of 50Hz pick up in a thermocouple measurement. If a third order LP filter is used for this, what should be its cut off frequency, if gain should be 0.001 at 50Hz.