What is converter transformer?
Diff b/w converter transformer and distribution transformer?
why we use converter transformer in place of giving supply
to drives?
Answer / jakeer
which will changes the frequency it is converter transformer.
Dist. transformer will changes the voltage.
| Is This Answer Correct ? | 0 Yes | 3 No |
what is difference b/w CFL and Ordinary lamps? which one is useful for power saving?
to calculate voltage drop of cable which current we consider that means full load current or panel size?
hi....I am from india..i have completed my engineering in electrical and electronics field with 58.4% and my IELTS score is 5.5 bands....Recently i received my I-20 in computer and information science from Troy university in Alabama.On 18th i have a visa interview can u please tell me what type of questions i have to answer ??????
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
Do power transformers have an Automatic Voltage Regulator (AVR) just like the alternator/generator in a power system?
WHAT IS THE DG OIL SPECIFICATIONS AND WHAT IS THE DIFFERENCE BETWEEN THE DG OIL AND TRANSFORMER OIL
What is the ideal position cooling fan inside the dc motor?
Energy metering: On the property I am renting, the supply voltage is 2 x 110 volts. These 2 x phases enter a energy meter which then exit the meter to over head lines to my house. Question 1. The meter is single phase 240 volts but is being used as 2 x phase(2 x 110volt), is this acceptable? if not, please give me the reasons. The meter details are as follows: 60Hz 15amp Imax 100 amp Kd 3,6 Wh/R 1 fase 3 hilos Model FX 231. I think it was manufactured in Brasil From this meter, the cables run along over head aluminum conductors,I estimate the cross sectional area to be 25mm diameter, but the neutral is only about 10mm square diameter, which cover a distance of 170 meters and then terminate with an underground cable of 65 meter length, total length = 235 meters. There must be a huge voltage drop over this length. This line is protected with 2 x 200 amp aluminum fuses after the meter, there is no main switch in the distribution board. These 2 phases connect directly onto 2 busbars. Surely the neutral should be the same size as the conductors if not more? Question2. What are your thoughts about this installation, should there be better protection, is the neutral too small? During the night, the lights dim then brighten all the time, this cannot be good for my electrical appliances. In my home, I only have a small electric geyser and fridge, my stove works off gas. But when i use other appliances like the washing machine or microwave oven, the light dim. The internal wiring of this house is done with solid hard drawn copper wires and of course, they have to be under rated. I am a retired electrician by trade, but not on the metering and over head mains side, my experience is on the factory maintenance side of things. Your expertise on these matters will be greatly appreciated. Please inform me how to rectify or make any improvements Kind regards, my power bill is very expensive, so I need to know how to bring it lower. Kind regards, Brian
if we increase frequency of line, then how will string efficiency varies with it.
Write down the design procedure of commutaj.
Why transformer use to generator neutral earthing purpose ?
How to calculate capacitor bank size at a load 800kVA.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)