what will happen if field winding supply of synch generator
accidently got disconnected?
Answers were Sorted based on User's Feedback
Answer / ibrahim
if field supply got tripped generator behaves as an
induction generator
Is This Answer Correct ? | 1 Yes | 0 No |
if field winding is disconnected then generator is not
build up bcz there is no any flux in the air gap so no flux
will be cut by armature conductor and at the same time no
emf will be induced
i think raghavendram wrong bcz obove condition occur when
prime mover is disconnected and excitation remains on..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pankaj agarwal
there are two scenarios one in which it is running in
islanding and other in which it is interconnected with
other system. in case one as field is cut there will be no
supply of exciting current and terminal voltage will fall
to zero. also turbine will tend to overrun as there is
sudden removal of load.
in case two as it is interconnected the stator is still
excited and it will behave like induction generator.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raghavendran
If Dc Excitation to the field winding got tripped, then a
condition occurs where the syn. gen draws power from the
grid and starts behavingas a motor.Though this condition is
not allowed to persist, and the system is isolated from the
grid.
Is This Answer Correct ? | 1 Yes | 2 No |
why neutral grounding transformer is used for generator and why it is not used for transformers?
what is use of lockout relay in ht voltage
what are the ratings of sockets?
How you calculating the 30 Hp 3 phase AC motor of power what size of cable is used for this motor?
why booster transformer is used in sumpners test conducted on transformer????
what is corona ?
WHAT ARE THE SITE TEST APPLIED ON A SURGE ARRESTORS? DO MEGGER TEST APPLIED ON SURGE ARRESTOR? IF YES THEN WHAT ARE THE ACCEPTED IR VALUE REQUIRED FOR SURGE ARRESTORS FOR VOLTAGE LEVEL 11KV, 33KV, 66KV 132KV, 220KV AND 400KV?
how do u calculate CT rating for 10 mva transformer
Witch do depand of Power factor and theory of power factor?
why rotor winding in induction motor is not earthed. normally we uses star winding in rotor .why?
3 Answers Anglo Platinum, TATA,
why all selected supply voltages are multiple of 11.i.e440,11 kv,33 kv,66 kv,110 kv etc
What are the methods used to improve powerfactor ?