for 500mw power production how many range of transformer
set in unit please reply if three transformer use .
Answers were Sorted based on User's Feedback
Answer / gangadhar
Dear friend answer is in que only.
For 500mw generation you may use 4 nos 125MAV transformer or
2 nos 250MVA transformer.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / umar
Taking power factor = 0.8
so MVA rating for 1 transformer will be =500 / 0.8 = 625 MVA
if three no. of transformers are used then rating of each
transformer will be 208 MVA.
| Is This Answer Correct ? | 0 Yes | 2 No |
How to select the gauge of wire for winding of motors? How to select number of turns for winding of three phase induction motor?
generally in LT and MV motors we are using 3.5Coresx16,25,35,50 etc cable for supply.although motors is earthed at two point and having all protection.then why we are using that 1/2 core for earthing the motors.while in HT cable we are using only 3core cable for motor supply.generally lt and mv motors are delta connected and ht motors having star connection.whethere it is having any relation with winding connection( star or delta).all motors i am talking about are dol only.can anybody solve my confusion.thanks...
what are the types of starter ?
25 Answers Andhra Sugars, Bhel, Eveready, HyFun Foods, Jindal, ME, Valeo Lighting Systems India Private Limited,
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
Why capacitor is blow when I am starting motor ?
54 Comments Alok and Bhanu play the following min-max game. Given the expression N = 38 + X*(Y – Z) where X, Y and Z are variables representing single digits (0 to 9), Alok would like to maximize N while Bhanu would like to minimize it. Towards this end, Alok chooses a single digit number and Bhanu substitutes this for a variable of her choice (X, Y or Z). Alok then chooses the next value and Bhanu, the variable to substitute the value. Finally Alok proposes the value for the remaining variable. Assuming both play to their optimal strategies, the value of N at the end of the game would be?
how to check avr of dg set of 125kva
which one is the most common system for secondary ditibution
how dose servo motor works
Tell me about Tesla.
If UG power cable both ends are to be earthed or what? If not why?
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)