for 500mw power production how many range of transformer
set in unit please reply if three transformer use .
Answers were Sorted based on User's Feedback
Answer / gangadhar
Dear friend answer is in que only.
For 500mw generation you may use 4 nos 125MAV transformer or
2 nos 250MVA transformer.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / umar
Taking power factor = 0.8
so MVA rating for 1 transformer will be =500 / 0.8 = 625 MVA
if three no. of transformers are used then rating of each
transformer will be 208 MVA.
Is This Answer Correct ? | 0 Yes | 2 No |