what happens if we are having very very high cavity and
flashing in a control valve..??? is it stops
working...immediately... or eroded...slowly
Answers were Sorted based on User's Feedback
Answer / gk3000
Valve does not stop immediately, but of course, due to
cavity / flashing, there will be a great impact on the
valve body. This case, you need to consider some solution
to lessen this phenomena. One may be putting a restriction
on valve inlet, or changing the trim construction of the
valve, or using a high grade material.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / www.islamqa.com
Actually the valve will not stop working, but as a result
of continous errosion it will be useless and you will need
to change the valve completely.
talking about solution need more details about the
situation but here is the basic guide lines:
# To avoid flashing:
====================
1 - valve selection with high Fl.
Fl:valve pressure recovery coefficient, and this introduced
by MASONILIAN as: Fl=(P1-P2/P1-Pvc)^.5 - and Fl max is 1.
where FISHER introduced Km =(P1-P2/P1-Pv) - and this is a
valve parameter presented by vendor and it's calculated by
lab tests, and usin Km we can get allowable(P1-P2) which
will not cause flashing.
2 - using anti cavitation trim, which generate multi vena
contracta points in the presuure profile, and this prevent
pressure drop below Pv.
3 - To cool down the process material to make Pv very low.
4 - To change the valve position to another place with high
pressure, to make pressure drop through the valve away from
PV.
And anyway if there is no escape from flashing, it's better
to sustain flashing within the valve to assure that we will
not have a cavitation when pressure recover, and liquid can
be recovered and bubbles can implode any other place away
from the valve.
and this can be achieved by heating up the process liquid
so we raise Pv, and a good indication for us to be sure
that flash will be sustained is p2, as we can know P2 at
downstream pipeline and make sure that it's below Pvc of
the process liquid.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 2 Yes | 0 No |
What is actuator what is motorized control valve?
ABB DCS (AC 800 M)redundency take howmany milliseconds to switch from master controller to slave?should be less than DCS scanning time?
why we use negative 24vdc to a proximeter
what is the difference b/w magnetic flow meter&mass flow meter? which one is best?
Actual using of tube bender to bend 2 opposite 90 deg at correct measurement center to center of tubing.
T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
hay friends, i am in trouble to understand PID controller. several times i have study but it is not clear to me have you a simple way to understand.
can we connect instrument earth pit to electrical earth pit, if not why?
what should be minimum length and size of impulse line for steam flow orifice and feed water orifice? asked by sanjay parihar
EXPLAIN SOME IMP QUESTIONS AND ANSWERS ON TOPIC ELECTRONICS,INSTRUMENTATION.........
why we use by pas on a positioner? When can a by pass be not used on a positioner ?
how does pressure is converted into milli amps in pressure transmitter? plzzz explain practically
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)