How can we do megger test of cable??
Answers were Sorted based on User's Feedback
Answer / sridhar nayak
by the help of tester the insulation of the cable canbe
measured. the simple technique is just raotate the handle
of the megger and place the test prod one on conductor and
other on the insulation it should not show less then 2mohms.
Is This Answer Correct ? | 16 Yes | 2 No |
Answer / savarkarshriram
If cable is rated for 1.1KV the megger test( Insulation
resistance test) is done with use of 500V or 1000V.
The test probes are connected across each phase , neutral
and ground terminal so that it covers all combinations.
If it is HT cable then 2000V IR tester is used. with the
same method as explained above.
Thumb rule for minimum value is 1M ohm per KV of rated
volatge of equipment
( Mind you megger is name of company and not name of test
so engineers should use term insulation resistance rather
than megger)
Is This Answer Correct ? | 3 Yes | 0 No |
What is systematic error?
What is best method of Calculating Short Circuit current in power system network.
fog produced due to?
Can I use 1 phase power supply to run 3 phase motor? If yes, how?
why when i start my diesel generator it takes 1 minute or less then stop, and i checked the oil sensor is ok and when the generator start i can get 220 voltage but it it is stop after 1 minute or less, how can i solve this problem?
what is the different ratings of ACB/VCB/SF6 which is used at HT side
What is type of transformers?
can i connect the two phases of scott connected transformer,if not why?
How many 2 ton window A/c can runs on a 125 KVA generator?
some practicle study shows that the reactive power at the receiving end is not equal to the reactive power at the sending end.But according to theory the reactive power is exchanged by different parts of the network – capacitors and reactors permanently, but is never consumed or produced. Then Where that reacrtive power loss occuring?is there any formula to calculate reactive power loss?
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?
what is difference between earth fault& restricted earth fault.