What is the function of UV coil ACB?
Answers were Sorted based on User's Feedback
Answer / satya dev
Under voltage coil is a protection relay which will give
the triping command to ACB during the Low Voltage in the
electrical system.uring the Insatallaion & commissioning of
UV Relay its need to set the Voltage Limit for it
operation.
Is This Answer Correct ? | 92 Yes | 13 No |
Answer / guest
If you want the ACB to remain in ON position than the under voltage coil must be powered.
Like in the case of ACBs of generators.
If for some reasons the generator fails than we want the generator to be isolated from the system than here we use an under voltage coil ACB.It means if NO supply to under voltage coil than you cannot ON the ACB.
Is This Answer Correct ? | 40 Yes | 9 No |
Answer / ashok h t
UV coil used for only under voltage protection in acb
Is This Answer Correct ? | 13 Yes | 8 No |
Answer / naganath jamadar
The UV coil main functions in ACB under voltage and over voltage protection because some electrical equipments working following voltage so we are set a under voltage 380 volt and over voltage 440 volt between 380 to 440 breaker will be tripped than safe the valuable equipments
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / satya dev
UV coil is a one type of feeder protection device and The main function of UV coil is to safe the feeder and equipment,s during unbalancing of power circuit. It is installed in the ACB and set the required Pick up and drop value of voltage in relay.so the beyond the set value coil will be energize and trip the ACB.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / navdeep patil
An Under Voltage coil is used to remotely trip a circuit breaker and some switch disconnectors. Schneider Electric uses the abbreviation MN for Under Voltage coils. An Under Voltage coil has to have a voltage applied to it to enable the device to close, and have the supply removed from it to trip the device.and also provide protection against under voltage.
Is This Answer Correct ? | 1 Yes | 0 No |
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
What is the difference between earthed & unearthed system?
what is the difference between Resistance VS capacitance
Connection diagram for KW meter and Kva meter
Do you know how to connect a motor of different H.Ps?
why humming sound occured in h HT transmission line
why we not used 11kva as a direct our electrnics component.
In CT,which terminal(s1,s2) need to be grounded?
What is Skin effect in Cable?
what is the difference between earth and neutral.
how to prepare PPM schudule