what is the difference between Resin Cast CT and Oil cooled
CT?
Resin Cast CT and PTs are usually used in indoor
switchgeear 11kv or 6.6kv substations etc. whereas Oil
cooled CTs are used in outdoor substations viz 11kv or 33kv
switchyards.
Difference is that Resin cast are solid cast type. Oil
cooled are those immeresed in Transformer oil and sealed.
In larger capacity CTs where cooling is required then oil
cooled CTs are preferred.
| Is This Answer Correct ? | 10 Yes | 0 No |
Why Humming noise originated in Starter motor and how it was generated ?
What happens if you give supply to the rotor of three phase induction motor?
why the starting current of a motor is high?
With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.
Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA ?
How Can You Relate Power Engineering With Electrical Engineering?
what is the difference between ground, earth and neutral?????????....
why the flooring of substation is done with small pebbles or stones..?
Earth bits close or open. Which is correct
Why nutral wir used thinner than phase wire
what is diversity factor ? plzzzzzz describe me
what is DG A,B,C,D check?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)