why C T secondary are rating 5A generaly .
Answers were Sorted based on User's Feedback
Answer / n arunkumar
CT secondary is 5A in Low voltage systems because we need
more graduation in measurement of current.Moreover measuring
range is small in LT system. but in High voltage system, the
measuring range is more.we need more accuracy. so we prefer
1A secondary in HT system.
| Is This Answer Correct ? | 24 Yes | 2 No |
Earlier they were using electromagnetic relays and
meters.Hence for accuracy and workability higher current
was required. Now a days CTs of 1 A secondaries are
used ,as electronic meters and relays have replaced them
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / nagarjuna
most of the relays work at lower rating generally 5 amps.we
get more accuracy with small rating.so that relays r
generally 5 amps
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sobhuza, za
5A CTs are used beacuse they are cheaper than 1A Cts for
the same primary rating.I mean 600/1A CT is more expensive
than 600/5A CTs as more turns are in the former. 5A CTs
also imply that under full load conditions, 5A is flowing
between the CTs and the relays. Therefore there will be a
large volt-drop if the CTs are far away from the relays.
This is the reason why it 5A CTs are used for indoor
switchgear. Recall that the indoor switchgear houses the
relays as well so the CTs and the relays are closer to one
another. Therefore you will note that 5A CTs are not used
for outdoor CTs.
| Is This Answer Correct ? | 2 Yes | 5 No |
hai...... tis is Hemanth. jst now completed electrical engineering... i wanna to apper for ap tranco exam... plzz send me the previous q's paper link......thanx in advance.
how to calculate load if i have three phase & single phase connection from power transformer( in term of kw & kva).can i take single phase load/3 for total kw calculation
what do you mean by 1 ton in AC`s
36 Answers Bhel, Bosch, ITC Infotech,
what is the differenc between A.C. and D.C, which is more dangerious?
thyristor controlled APFC panel design parameter?
what happenes if two voltage source connected in parallel will be connected to load.
in alternator what is use of AVR ? how AVR is operating either AC or DC?
IP55 protection stands for
What is mean by hot and cold loop testing? What is the difference between them?
What happens to the terminal voltage of an alternator connected to a bus bar when it is suddenly disconnected from the bus bar??
at the time of starting back emf of a motor is zero.so how can it will start to run??
what is the cause of voltage dipp or swell in the transmission lines?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)