why C T secondary are rating 5A generaly .
Answers were Sorted based on User's Feedback
Answer / n arunkumar
CT secondary is 5A in Low voltage systems because we need
more graduation in measurement of current.Moreover measuring
range is small in LT system. but in High voltage system, the
measuring range is more.we need more accuracy. so we prefer
1A secondary in HT system.
| Is This Answer Correct ? | 24 Yes | 2 No |
Earlier they were using electromagnetic relays and
meters.Hence for accuracy and workability higher current
was required. Now a days CTs of 1 A secondaries are
used ,as electronic meters and relays have replaced them
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / nagarjuna
most of the relays work at lower rating generally 5 amps.we
get more accuracy with small rating.so that relays r
generally 5 amps
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sobhuza, za
5A CTs are used beacuse they are cheaper than 1A Cts for
the same primary rating.I mean 600/1A CT is more expensive
than 600/5A CTs as more turns are in the former. 5A CTs
also imply that under full load conditions, 5A is flowing
between the CTs and the relays. Therefore there will be a
large volt-drop if the CTs are far away from the relays.
This is the reason why it 5A CTs are used for indoor
switchgear. Recall that the indoor switchgear houses the
relays as well so the CTs and the relays are closer to one
another. Therefore you will note that 5A CTs are not used
for outdoor CTs.
| Is This Answer Correct ? | 2 Yes | 5 No |
WHY THE RATINGS OF THE TRANSFORMER IS 33KV WHY NOT OTHER???
what is bushing in transfermor
7 Answers Bokaro Steel, Visa Steel,
we done magnetic balance test for 33KV /440V transformer in our company , but the ratio out is confusing us Voltage applied in RY = 440 , at RB = 320 and YB = 60 RY 440 = ( RB + YB ) 380 only Please let me know what type of problem is it.
brief notes on ammeters
the rating of fuse wire i always expressed in what?
WHAT IS MEANT BY SYNCHRONISING IN GENSETS
Why electric sock occur to human or any lives ?
what is the use of Reactive power
if we have 380 KVA DG. how to calculate Power Factor. With detailed formula
The power dissipated by a resistor of 10ohm when a current of 2A passes through it is:(a) 0.4W(b) 20W(c) 40W(d) 200W
why to need a electrical earthing?
how many stairs have you climbed while you were coming
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)