why C T secondary are rating 5A generaly .
Answers were Sorted based on User's Feedback
Answer / n arunkumar
CT secondary is 5A in Low voltage systems because we need
more graduation in measurement of current.Moreover measuring
range is small in LT system. but in High voltage system, the
measuring range is more.we need more accuracy. so we prefer
1A secondary in HT system.
| Is This Answer Correct ? | 24 Yes | 2 No |
Earlier they were using electromagnetic relays and
meters.Hence for accuracy and workability higher current
was required. Now a days CTs of 1 A secondaries are
used ,as electronic meters and relays have replaced them
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / nagarjuna
most of the relays work at lower rating generally 5 amps.we
get more accuracy with small rating.so that relays r
generally 5 amps
| Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sobhuza, za
5A CTs are used beacuse they are cheaper than 1A Cts for
the same primary rating.I mean 600/1A CT is more expensive
than 600/5A CTs as more turns are in the former. 5A CTs
also imply that under full load conditions, 5A is flowing
between the CTs and the relays. Therefore there will be a
large volt-drop if the CTs are far away from the relays.
This is the reason why it 5A CTs are used for indoor
switchgear. Recall that the indoor switchgear houses the
relays as well so the CTs and the relays are closer to one
another. Therefore you will note that 5A CTs are not used
for outdoor CTs.
| Is This Answer Correct ? | 2 Yes | 5 No |
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
what happens if sf6ckt breaker gas pressure is high or low about the actual rating of gas pressure(5kg/cm2)
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
Where can I get Iidian straderd specifications for electrical items or works in web? please help me.
Between AC generator(alternator) and DC generator which can be designed for high voltage and why?
How to convert 110 volt alternating current to 12 volt direct current
what is the senstivity and stablity? what is different?
why supervision relay is used in incoming feeders?
Approach of a cooling tower is the difference between temperatures of what factors?
What happens if there is no nuetral in the power system?
what is ballast
Single phase and threephase power calculation
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)