The neutral to earth connection in my industry is showing a zero reading
(shorted). I have a machine which has to be installed where neutral to earth is
not shorted and shows a leak voltage <3 Volts. Please suggest me how it is
possible.
Answers were Sorted based on User's Feedback
Answer / bikash
SImple earth is always in zero potential, so when u connect
neutral to earth or measure voltage it will show zero
voltage. But actually neutral is the return path or it is
required for completing a ckt. It shows the unbalaced
system voltage. If system is balaced neutral will show zero
voltage or otherwise it will show voltage. So check load
condition.
| Is This Answer Correct ? | 6 Yes | 1 No |
Hi Ravi
Of course if you have your power supply neutral earthed
from supply side (transformer or generator neutral) you
will get zero potential at between the neutral and earth at
any point of the distribution circuit ; you should get more
information about the type of your earthing system (IT, TT,
TN-S or TNC)
You can find more details at Schneider site or ABB sites
or directly from IEC 60364-5-54 Electrical installations of
buildings - Selection and erection of electrical equipment -
Earthing arrangements
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ravi mittal
The problem has been solved now. I have installed an isolation transformer
which has solved all the issues.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ravi mittal
Dear Bikash,
I am thankful to you for taking interest in answering my
query.
Actually, I have an equipment for which I have been clearly
indicated to not have neautal and earth shorted. If done
so, the equipment may have problems in future. When we
check with the multimeter the neautral to earth is showing
as shorted which gives a zero reading which is actually not
shorted. What can I do in this case where can I either get
a 0 reading (when not short) or <3 volts reading? Is there
a fault with my wiring? Some electricians say that this is
a usual phenomenon in industrial areas. If the phenomenon
is usual, is there a device which can be installed to
rectify this problem.
Thanks and regards,
Ravi Mittal
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kannan
Cheech your earth value as per standard. If not install new
earth rod. It may solve your problem.
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / nadir
Possibly your machine required an IT wiring which is unearth neutral. Your machine may required only a PE and the PE electrode shall be installed at a distance of 1.5 longer than your transformer/ neutral earth electrode length.
The isolation transformer will also create harmonics and required to dissipate.
| Is This Answer Correct ? | 0 Yes | 0 No |
wat do knw aboot circuit breakers ?
What is the de rating factor of cable? What is the importance of the de rating factor in cable select
When color of silica gel will gets change from blue to pink from Top to bottom?
how many earthing is required for sever room?
what is the difference b/w bus reactor and line reactor?
how much percentage(%) of load can feed in power transformer?
in a plug point why the hole size at the top is large?
Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?
why do we lay up the core of a cable?
Give me the calculation steps to design an electromagnet to be work in 230V 50 Hz AC Supply. Also give force that is created by that electromagnet when it gets energized.
What is the ideal power factor?
we have 350 kva capcitor bank which is not showing KW. dose capacitor shows kW OR not.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)