Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why inverter rating in KVA?

Answers were Sorted based on User's Feedback



Why inverter rating in KVA?..

Answer / seank

True rating of a power supply is the amount of Voltage and Current that is flowing through the device.

If inverter rating is in kVA then the manufacturer is publishing ratings without assuming a power factor so the inverter could be used by rating on loads with potentially widely varying power factors.

This kVA would be best described by the Apparent Power(S).

If Apparent Power (S) is under estimated then it is possible the power supply will be undersized.

kVA to kW calculation
The real power P in kilowatts (kW) is equal to the apparent power S in kilovolt-amps (kVA), times the power factor PF:

P(kW) = S(kVA) × PF

Is This Answer Correct ?    3 Yes 0 No

Why inverter rating in KVA?..

Answer / sreeknp

we cant predict the pf of load ,dependig upon the load kw
changes so we can say current supply and voltage only ,for
example a300va unit to which five tube can be connected
since its pf is .4 then ups will be over loaded if one ortwo
addtional tube will burn this ups i think ur doubt is cleared

Is This Answer Correct ?    11 Yes 9 No

Why inverter rating in KVA?..

Answer / saravanan.p

The inverter rating is in KVA because of in any active
components (like transformers, D.G, inverters etc..), the
power is calculating based on the output of the devices. At
the output terminals, no losses are considered causing by
active/passive loads (R,L,C). This is not depend on the
input.

But in the passive components (like motors, engine etc..),
the output is taking by means of input.

The output is always lesser than the input due to losses.
So the motors are denoted in the unit of KW.

Is This Answer Correct ?    6 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

Explain about technical and non technical losses in distribution system?

0 Answers  


we have one pumping station and 4.6 MW 7 no.s synchronous motors.so there is no required HT capacitor to improve power factor.But we have two no.s of 25 Mva power transformer connect to distribute the power for motors connect with 220 kv line.So i have required the HT capacitor to improve power factor at HT side i mean power transformer bus side.So please suggest how much HT capacitor banks required for same.

1 Answers  


how to flameproof electrical motor on the shaft?

0 Answers  


why does voltage generation at 11 kv?

2 Answers  


in case of transformer the power factor is depend on input or the output

1 Answers  


A motor works on 30 killo watts.how much ampers will be required if it works on 440volts?

5 Answers  


WHAT IS MEANT BY EMBEDED SYSTEM?CAN WE CALL PLC AS EMBEDED SYSTEM?

2 Answers  


what is corona ?

3 Answers  


what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?

0 Answers  


Diffrectiate between earthing and neutral

6 Answers   TATA,


what are the reasons for overheating in electrical machines?

3 Answers  


explain the types of drives

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)