After synchronization with grid how to maintain the
power factor in lagging or in leading? if lead of lag what
is the problem?
Answers were Sorted based on User's Feedback
Answer / m.vasudevan
By using a capacitor bank ppower factor lagging or leading
can be maintained. Leadin power factor is the problem. If
Power factor is leading, the reactive power of total power
export to the grid is high and active power content will
become less.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / k.prakashchandra
Pf lagging means over-excitation ,leading pf is caused by
under excitation.Maintain pf at 0.95 t0 0.98 lagging by
varying the excitation .
Is This Answer Correct ? | 2 Yes | 0 No |
both lagging and leading p.f will badly affect the system
we have to maintin unity p.f.
lagging and leading p.f will take more current from the
alternator for the same equipment.
eg: power taken by a motor = v*i pf
= 230*20*1= 4600 w
suppose if the p.f is .6 either lagg or lead
in order to get the same power to motor it will take more current ie more than 20 amps.
Is This Answer Correct ? | 2 Yes | 3 No |
PLC Training in chennai | PLC Training institute in chennai, PLC Training center in chennai | Best PLC Training in chennai | PLC Training course in chennai | SCADA Training in chennai | PLC Training in india
how to determine capacitor bank capacity of one plant..
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
what is power factor?
8 Answers Adani, Blue Star, Power Control,
Is it necessary to seperate the DG earth grid with Electricity Board earth grid for protecting the DG set. if yes why?
Why IGBT is very popular nowadays?
what is formula of dc current and resistance.
which tap of the transormer you will use in critical condition(worst)?
Why a tesa lamp is glow between two phase?
Your B.tech marks is being given in CGPA grade. How is it calculated?
(In MEP services) HVAC in AC Plant room what else can we provide if the chiller is not considered?
What are the differences between single phase and three phase?