In 6600/√3/110/√3v voltage transformer,how much output
voltage in open delta transformer,after removing 1-phase of
primary side on transformer?
Answers were Sorted based on User's Feedback
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V.
If all three H.V.phases are connected the voltage between secondary terminals[in series] is 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V.
| Is This Answer Correct ? | 0 Yes | 0 No |
The open-delta connection it is actually 2 single phase transformer in series.
The voltage between two high voltage terminals it is 6600 V and each secondary
phase presents 110/√3 V[ some time even 100 or 110V].
If all three H.V.phases are connected the voltage between secondary terminals[in direct series] is 110/√3<0o +110/√3<120o=-110/√3 V<240o or oppositely connected 110/√3<0o -110/√3<120o=110 V<30o .
If the removed phase it is an extreme one then only one transformer stays connected [two voltages at ends] and the voltage is 110/√3 V.
If the removed phase it is the middle then both transformers stays connected with only one 6600 V and the voltage is 2*110/√3/2<0o=110/√3 V[or 110 V] for direct connection or 0 if they are oppositely connected.
| Is This Answer Correct ? | 0 Yes | 0 No |
electical engg basic question
How to protect the water pump by no load running.
Can We Apply DC POWER To Transformer???? And Why????
in railways why we use the power in 10,20 30kv,why not in the multiple of 11kv
Define thermal resistance in the context of power amplifier.
What is the necessary and sufficient condition for stability.
I just purchased a 4 position cam switch to be used to operate a 3-speed blower motor. The motor is a 10 amp motor and has 3 wires that are used to control speed. The cam switch was rated at 660V 20 amps but when I received it, I noticed that it has AC-15 operational current rating (Ie) of 4/5 amps. If I am reading the label correctly. the 4/5 amps is related to 440v/220V (Ue). Other ratings are AC-3: 5.5A, AC2: 7.5A and AC-4: 1.5A. My questions are 1) Is it safe to use this switch with the motor I have 2) what is the difference between the 20 amp Ith ratting and the Ie operational ratings?
if we want to convert the two 12 V DC batteries in parallel for UPS ? what would be the result ? which is better for a UPS , connect two batteries in series or connect them in parallel ?
Why and when NGR panel required. Is it necessary to design a NGR panel for a 6.6kV Alternator paralleling with Grid????
apti mainly on logical reasoning, verbal and non-verbal ability (70 percent) and remaining technical. I was in ee but technical had mech ques like on turbines and welding.
why near the transformers, the Jelly(small white colored rocks)are poured.and what are conditions for that?
In a star to star transformer can we use a common neutral for both star connected primary and secondary
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)