why anti pumping relay is not given to tripping coil of the
breaker? why only to closing coil?
Answers were Sorted based on User's Feedback
Answer / karna
Actually in Breakers Closing coil and Trip coil are
operated on Pulse command (i.e just initaion is enough,
continous supply not required). Anitpuming Means once the
breaker is colsed ,again if anyone ( Auto Command, Through
TNC switch ) can close it will not close because in closing
circuit Antipuming NC will be in series, Once the breaker
close means antipuming will activate unitll trip command
given by us.
Tripping coil plays major role in Circuit brakers, because
if any faults ( i.e O/L, E/L, short Circuit etc..)occur
breakers has to tirp. For trip we can do manaully at any
time.
Is This Answer Correct ? | 2 Yes | 0 No |
Closing is on command and tripping is either on command or
auto .You are testing the circuit by closing the CB using
the control switch
Is This Answer Correct ? | 0 Yes | 0 No |
can we check the resistance of earthing electrode while it is connected with the neutral of UPS system
IT IS DESIRABLE THAT THE INCOMING MACHINE SHOULD BE A LITTLE FAST AT THE TIME OF SYNCHRONIZING.EXPLAIN?
Good day everyone,currently in our premise we using 30kw slip ring motor with resistance bank which we use as forward and reverse at conveyor bar handling. So,my question is how do we calculate the resistance bank which is suit the motor. Kindly,assist me... thank you
what is the pre commissioning test to be carried out on LT power panel at site?
role of shunt coil in circuit breakers
two TG running in parallel at equal load.one TG CB tripped in reverse power relay.after tripping found its excitation was on & turbine running at rated speed.Please clearify why that TG tripped in reverse power ?
Why carbon brushes are used in motors?
diffrence between abcb and mocb
What is difference between ball screw and lead screw.
Why is the earth pin in a 3-pin plug the longest and the thickest?
What do you mean by phasors?
how to improve power factor correction?