why anti pumping relay is not given to tripping coil of the
breaker? why only to closing coil?
Answers were Sorted based on User's Feedback
Answer / karna
Actually in Breakers Closing coil and Trip coil are
operated on Pulse command (i.e just initaion is enough,
continous supply not required). Anitpuming Means once the
breaker is colsed ,again if anyone ( Auto Command, Through
TNC switch ) can close it will not close because in closing
circuit Antipuming NC will be in series, Once the breaker
close means antipuming will activate unitll trip command
given by us.
Tripping coil plays major role in Circuit brakers, because
if any faults ( i.e O/L, E/L, short Circuit etc..)occur
breakers has to tirp. For trip we can do manaully at any
time.
Is This Answer Correct ? | 2 Yes | 0 No |
Closing is on command and tripping is either on command or
auto .You are testing the circuit by closing the CB using
the control switch
Is This Answer Correct ? | 0 Yes | 0 No |
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
WHAT IS MOBILE SUB-STATION? & REALLY BENEFIT IN INDIA
what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
what is formula in determining the size of Circuit Breaker for transformer with the following specifications. 7 units of 1600 volts (primary) and 400 volts (secondary). Both Primary and Secondary will have a circuit breaker which is SF6. What should be the Switchgear Main Breaker Size anf the sizes of each brances Circuit Breaker for Primary.
what is DG A,B,C,D check?
What is the function of RCBO? What are the different sensitivity ratings & each application?
what happens when power factor leads or lags to electical or home appliances
which relay is used for both detection & correction?(there is only one relay)
what is the suitable voltage of transmission line to transmit 10000w power through 250 km. (a)11kv (b)33kv (c)66kv (d)132kv ]and please tell me whats the logic behind it
How much should be the specific gravity of a DG set battery Electrolyte.
What is mean by PID controller? And what is its Long form?