Answer / pradyumna chandra panda
k prakaschandra is correct. * 35 sqmm 3core aluminium conductor is sufficient because 630KVA transformer full load current is 31.5 amp and 35 sqmm al conductor can take 70 amp current.
| Is This Answer Correct ? | 5 Yes | 2 No |
what is a composite error in current transformers, why occurs & in which it will occur i.e, either metering ct/ protection ct
we have consol make 3 phase servo stabilizer for cnc m/c. while installing the earth neutral voltage is 1.7 volts at stbilizer off condition and when stabilizer get on en voltage reaches 4.8 volts (new earthing is done and neutral is helthy condition all phase to neutral volts 440,442,441 v)why this happen.solution for cause.
What is dynamo?How it works and what is the function of dynamo in a DG.
how you taken aotitude test
define the non synchoronism of synchoronous machine in general g or m??
What is difference between Harmonic and Non harmonic Capacitor Bank?
operation of protection relay watchdog contact?
How can calculate thermal overload in relay?
what is meant by excitation which supply is used whether ac r dc in the lab applications
What do you mean by phasors?
Where is 2 phase supply used commercially?
We know no of electron and proton in atom but how many Neutron are thire in an atom ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)